Difference Between B Curve & C Curve in MCB.
Answers were Sorted based on User's Feedback
Answer / raghavendran
MCB's have tripping curves like B,Cand D.
Curve B type of MCB's are used where maximum sensitivity is
needed and the initial starting current is 3 to 5 times the
rated current.
curve c MCB's are used where close protection is not
required and the starting current is 5 to 10 times the rated
current.these may be used while tripping the circuit due to
high starting inrush current.
curve D MCB's are used where the starting current is very
high 10 to 20 times the rated current, like high capacity
motor installation where initial starting voltage dip may be
very high.
| Is This Answer Correct ? | 98 Yes | 4 No |
Answer / anil tandon
The MCBs are classified as per the Holding Currents and thus their usage are define accordingly,
B-Curve MCB:- They have a Holding current of 2 times of rated current and are used for Lighting Loads
C-Curve MCB:- They have a Holding current of 5 times of rated current and are used for motoring Loads.
The MCBs are classified as per the Holding Currents and thus their usage are define accordingly,
B-Curve MCB:- They have a Holding current of 2 times of rated current and are used for Lighting Loads
D-Curve MCB:- They have a Holding current of 10 times of rated current and are used for High Inrush currents E.g -Control Transformer etc
| Is This Answer Correct ? | 47 Yes | 6 No |
Answer / arshath
B curve using for domestic
C curve using for industrial
| Is This Answer Correct ? | 23 Yes | 5 No |
Why in KVA diesel engine? Why not KW
How to run 1ph motor(230 VOLTS its full load amps is 4.5 ampa))with 480 volts main(we didn hav neutral)Thn we go for step down transformer.Our load 10 amps,so we conisder this amps in primary are secondary side
what is the size of ht cable of 33kv ht line and transformers ratings are 1 Mva and 5mva.please send formula also.
which cable is preferred PVC OR XLPE for voltage from 220V to 11 KV with proper justification
what is the meaning of transformer short circuit test?
why did the BDV test in transformer?
2 Answers Jindal Steel and Power,
why we use four type of phase angle difference between pimary & secondry winding of a transformer & where we use them?
How is operate breaker failure scheme in substation
Define over current & earth fault ?how its functioning ?
What is the simplest formula to calculate the rotor diameter of a synchronous generator?
SUTIABLE FOR ohm's law super conductor
why do we need a 4th wire in 3phase 3wire transmission line
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)