Answer / raghavendran
MCB's have tripping curves like B,Cand D.
Curve B type of MCB's are used where maximum sensitivity is
needed and the initial starting current is 3 to 5 times the
rated current.
curve c MCB's are used where close protection is not
required and the starting current is 5 to 10 times the rated
current.these may be used while tripping the circuit due to
high starting inrush current.
curve D MCB's are used where the starting current is very
high 10 to 20 times the rated current, like high capacity
motor installation where initial starting voltage dip may be
very high.
| Is This Answer Correct ? | 98 Yes | 4 No |
Answer / anil tandon
The MCBs are classified as per the Holding Currents and thus their usage are define accordingly,
B-Curve MCB:- They have a Holding current of 2 times of rated current and are used for Lighting Loads
C-Curve MCB:- They have a Holding current of 5 times of rated current and are used for motoring Loads.
The MCBs are classified as per the Holding Currents and thus their usage are define accordingly,
B-Curve MCB:- They have a Holding current of 2 times of rated current and are used for Lighting Loads
D-Curve MCB:- They have a Holding current of 10 times of rated current and are used for High Inrush currents E.g -Control Transformer etc
| Is This Answer Correct ? | 47 Yes | 6 No |
Answer / arshath
B curve using for domestic
C curve using for industrial
| Is This Answer Correct ? | 23 Yes | 5 No |
WHAT IS THE FORMULA FOR CALCULATING CURRENT RATING(DIRECT IN GROUND OR AIR) OF ARMOURED(XLPE) CABLE OF 4C,16Sqmm?
WHY DISEL GENRATOR SET SHUT DOWN IN OVER LOAD CONDITIONS
How will you define capacitance?
What are the three major categories of error?
What is GIS (Gas Insulated Switchgear)
What is formula of capacitor for 1-phase power connection.how to improve PF. Suppose I want to connect capacitor in refrigerator to reduce power consumptions.
what is the min and max dc voltage for a dc system (110vdc)
On a 10 KVA UPS we have to provide a DC MCB for Battery bank of 16 nos (12 V 65 AH). What Shall be the current rating of DC MCB ?
6 Answers RR, TNEB Tamil Nadu Electricity Board,
Is there any calculation to find unknwon(unferroled) phases R Y B in alternator,3 phase motor anybody shoot my problem. how can we notice this is the respective phase?
why 3 phase motors are preferable over single phase motors ?
why rating of transformer is in KVA but of motor is in KW
how to find the resistance
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)