Can we use a Potential Transformer for Auxilliary Power
supply( Spring charge Motor, Lighting etc)?
Answer / k.prakashchandra
No. The output of PT is 110 V line or 63.5 V phase
usually.The capacity of PT is from 30 t0 500 VA, anyway not
more than 1 KVA.As PTs are also used for protection ,they
should not be used for power supply purpose.
Is This Answer Correct ? | 2 Yes | 0 No |
Is it true that IPT are more accurate than CVT for Measuring purpose?
WTA used cb?
. Is there a simple method to measure the horsepower of a small motor (1-3 hp) for a non-technical person
what type of relay has to be used for tripping the circuit from mains when a fault occur in a machine
Dear Sir, we met a disaster with our 62.5 kva genset, after rewinding we informed by our contract engg that due to return current coming in neutral & impropper earthing this happend. But after all set up & load balance we checked & found again we have about 20 to 32 amp return current on neutral. we have 12 airconditioner + 12 mini fridge on single phase line. Pl suggest any idea to solved this problem
Testing procedure of DG alternator stability test
in 220 kv substation,what is the mean of avr voltage reading? means at oltc temp. 36 the avr voltage was 109v.so what the mean of 109v
what is the function of closing coil in air circuit breaker?
what is mean by hvdc transmission technology .what is principle of hvdc transmission and technic of hvddc transmission .
what is the use of current transformer in power transformer secondary side.?its connectyed in WTI
How to calculate the cross section area for a 350 m cable, motor power is 26 kw???
we have a rewind motor of 2Hp,2800Rpm, 220Volt AC. how can we choose the running capacitor for this motor, any formula for that?