Why should we use Star-Delta connection in step down power
transformers?
Answers were Sorted based on User's Feedback
Answer / harishchandra
in Y the vL=1.73*vp
in delta vl=vp and current IL=1.73*ip
also for distribution required 230 n 433v so neutral is
required so we used y - delta conec.
| Is This Answer Correct ? | 23 Yes | 7 No |
Answer / hussain
Actually we use Delta-Star connection for step down to get
neutral in the secondary. The question is wrong , should
read why we use delta-Start connection , not opposite.
| Is This Answer Correct ? | 18 Yes | 7 No |
Answer / guest
1:--- actually we used delta -star connection in power
distribution transformer to provide the returning path of
current,because connected load does not balanced so
returning current goes to transformer star point through
neutral wire which always earthed.
2;---In distribution load is being different type like
single phase three phase etc so we have required neutral for
single
phase load which is only possible in star connection.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / pkv
actually delta star trnasformer used in step down
trnasformer to avoid earthfault give effect of over
current on hv side of the trnaformer
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / arindam
Delta is mainly used on low voltage side because its line voltage=phase voltage. if it is used on high voltage side due to high voltage in phase more insulation is required. But if it is star then its phase voltage = (1/√3)phase voltage. so if high voltage applied to line of star its phase value decrease by √3 times and comparetively less insulation is required. Hence star-delta is used for step down and delta-star is used for step up.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / rafeek
question is wrong,
normally we use delta-star connection for step down
transformer to prevent earth faults.
| Is This Answer Correct ? | 0 Yes | 4 No |
Answer / paramesh
Because starting voltage of the star connection is less
compare 2 other connections..........
| Is This Answer Correct ? | 6 Yes | 17 No |
how to decide the ratings of the MCCB,MCB in electrification.give me the proper thumb rule or procedure.
WHAT MEANT BY SEVICE FACTOR?
Alternators are invariably star connected why?
What is BUCKBOOST TRANSFORMER and Operation of Buckboost transformer?
HOW TO CALCULATE LV CABLE SIZING?
what is the different ratings of ACB/VCB/SF6 which is used at HT side
What is the knee point voltage of CT-100/5,15VA,5P20 ?
what are the reasons of low voltage during start the DG?
WHY NUTRAL GROUND SYSTEM USED IN 33KV SYSTEM
what is voltage rise and voltage drop?
IT IS DESIRABLE THAT THE INCOMING MACHINE SHOULD BE A LITTLE FAST AT THE TIME OF SYNCHRONIZING.EXPLAIN?
in alternator what is use of AVR ? how AVR is operating either AC or DC?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)