Why should we use Star-Delta connection in step down power
transformers?
Answers were Sorted based on User's Feedback
Answer / harishchandra
in Y the vL=1.73*vp
in delta vl=vp and current IL=1.73*ip
also for distribution required 230 n 433v so neutral is
required so we used y - delta conec.
Is This Answer Correct ? | 23 Yes | 7 No |
Answer / hussain
Actually we use Delta-Star connection for step down to get
neutral in the secondary. The question is wrong , should
read why we use delta-Start connection , not opposite.
Is This Answer Correct ? | 18 Yes | 7 No |
Answer / guest
1:--- actually we used delta -star connection in power
distribution transformer to provide the returning path of
current,because connected load does not balanced so
returning current goes to transformer star point through
neutral wire which always earthed.
2;---In distribution load is being different type like
single phase three phase etc so we have required neutral for
single
phase load which is only possible in star connection.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / pkv
actually delta star trnasformer used in step down
trnasformer to avoid earthfault give effect of over
current on hv side of the trnaformer
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / arindam
Delta is mainly used on low voltage side because its line voltage=phase voltage. if it is used on high voltage side due to high voltage in phase more insulation is required. But if it is star then its phase voltage = (1/√3)phase voltage. so if high voltage applied to line of star its phase value decrease by √3 times and comparetively less insulation is required. Hence star-delta is used for step down and delta-star is used for step up.
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / rafeek
question is wrong,
normally we use delta-star connection for step down
transformer to prevent earth faults.
Is This Answer Correct ? | 0 Yes | 4 No |
Answer / paramesh
Because starting voltage of the star connection is less
compare 2 other connections..........
Is This Answer Correct ? | 6 Yes | 17 No |
what r PID controllers?why they r used?what is there purpose?plz Explain in detail
How to calibrate or test an LT Air Circuit breaker 440 volts, 35 KA, 800 Amps ?
If one d.g. is unable to take full load of system, then second d.g. will take care of partly Load.for this condition RPM of both DG set should be equal.By using Synchronization panel RPM of dg sets are match, is it true?
if there is nutral in phase why we use earthing wire and grounding? even at fault condition the fault current flows to neutral (it is a lower path)
please send me previous year questions of jspl through which i could prepare myself for the test.
in dc transmission the frequency pi is zero, then how it will transmit communication signal?
explain harmonics in simple words..........
how to calculate the magnetizing current of ct ( 800A/1A) for Relay 64
How to calculate voltage drop loss in HT 11000 Volts XLPE Aluminium conductor cable. Any specific formula or Thumb rule
Why carbon brush used in dc motor also why its not used in ac motor?
take 100kva DTR( delta/wye ), what ll happen if we connect 11kv to LT side instead of connecting to HT side? will the DTR behave as a step up transformer or something else????
29 Which of the following breaking method save energy? A regenerative breaking B plugging C dynamic breaking D none of above