Answer / harishchandra
in Y the vL=1.73*vp
in delta vl=vp and current IL=1.73*ip
also for distribution required 230 n 433v so neutral is
required so we used y - delta conec.
| Is This Answer Correct ? | 23 Yes | 7 No |
Answer / hussain
Actually we use Delta-Star connection for step down to get
neutral in the secondary. The question is wrong , should
read why we use delta-Start connection , not opposite.
| Is This Answer Correct ? | 18 Yes | 7 No |
Answer / guest
1:--- actually we used delta -star connection in power
distribution transformer to provide the returning path of
current,because connected load does not balanced so
returning current goes to transformer star point through
neutral wire which always earthed.
2;---In distribution load is being different type like
single phase three phase etc so we have required neutral for
single
phase load which is only possible in star connection.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / pkv
actually delta star trnasformer used in step down
trnasformer to avoid earthfault give effect of over
current on hv side of the trnaformer
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / arindam
Delta is mainly used on low voltage side because its line voltage=phase voltage. if it is used on high voltage side due to high voltage in phase more insulation is required. But if it is star then its phase voltage = (1/√3)phase voltage. so if high voltage applied to line of star its phase value decrease by √3 times and comparetively less insulation is required. Hence star-delta is used for step down and delta-star is used for step up.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / rafeek
question is wrong,
normally we use delta-star connection for step down
transformer to prevent earth faults.
| Is This Answer Correct ? | 0 Yes | 4 No |
Answer / paramesh
Because starting voltage of the star connection is less
compare 2 other connections..........
| Is This Answer Correct ? | 6 Yes | 17 No |
How the unidirectional torque produced in dc motor
What should be the percentage increase in length of the dead end clamp for bus bar conductor (Hawthorn) after hydraulic pressing and what should be the applied pressure?
in case dc we mark as + ve & -ve..but in case a.c. we mark as ph&N...Y LIKE PLZ TELL ME
IF THE OUTPUT OF A 100KVA, 415V GENERATOR IS STEPPED UP TO 11KV WITH A 500KVA TRANSFORMER,CAN THE TRANSFORMER BE LOADED ABOVE THE SOURCE GENERATOR RATING?
How would you calculate power loss in a resistor?
what is the difference between changer, converter and transformer?
Define thermal resistance in the context of power amplifier.
why starter use to on a motor
Between AC generator(alternator) and DC generator which can be designed for high voltage and why?
What are the causes of electrical faults?
define the active power?
Dear Brother can u tell the proper size selection of cable & the fault level calculation of braker, busbar etc. pls mail me at azeemk30@gmail.com
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)