can i know how to design overcurrent setting and earth
fault for 11kv & o.433kv system assuming tx 1000kva.
Answer Posted / prakash.
First selected for ct ratio in HT panel.1000kva transformer full load current in primary 52.5amps.so ct ratio in 60amps(60/5).
Now relay setting for over current 55amps.
And earth fault setting 0.5amps in ct secondary amps..
| Is This Answer Correct ? | 4 Yes | 0 No |
Post New Answer View All Answers
how can we design robots
WHAT IS ELECTRICAL MAINTAINTENCE ?
What is the use of Surge Capacitor in LAVT?
What does the term “voltage regulation” means?
I need the recommended size for a 3 phase transformer at 13.8 KV Primary and connected loads of 3000 kVA at 4200 volts and 2375 kVA @ 480 volts AC.
WTA used cb?
I have a small system with two motors that are running on 380 vac, 60 hz. These motors are expensive and I usally get them from Brazil. I am adding another motor to the system, but I want to purchase a 480 vac, 60 hz motor to use. It will be on a VFD that is rated fro 380 thru 480. Is this posible and will I have to use a larger motor and derate it?
distribution is maximum done by a)radial b)network c) parallel d)b & c
prove that power consumed in 3 phase delta system is 3 times as compared to 3 phase star system
why we are not giving the zone 1 trip command to the master trip relay
Operation carried out in thermal power stations?
Trafo ratio is 11kV/6.6kv,Vector group is YND11. What will be the effect if secondary is used for earthed system.
In case of salient pole alternator when number of poles are 4 or more than 4 it helps the flux wave to be sinusoid as air gap length is increased from center to tip , but if the number of poles are 2 how does the flux wave is sinusoidal?
A TRANSFORMER 440/400V,DELTA/STAR CONNECTED.THE NEUTRAL CONNECTED WITH GROUND CABLE THAT IS DIRECTLY CONNECTED TO THE PANEL,FROM PANEL IT IS CONNECTED EARTH PIT.IS IT RIGHT? IF IT IS RIGHT LEAKAGE CURRENT AFFECTED.SECONDATY IS PROTECTED WITH EARTH LEAKAGE RELAY.
how can maintain the power factor and why and this is how do work tell us