what is the reason for flow fluctuations happen on
differential flow transmitter during in service
Answers were Sorted based on User's Feedback
Answer / seth
Change in process pressure, restriction in one of the
sensing lines, rapid change in temperature, noise in the
signal being returned to the source of indication. (Check
for noise in the shielding-blow down sensing lines-check if
the process media is at the correct operating temp.-make
sure the equalizer valve is closed and the sensing (hi and
lo) lines are open.
Is This Answer Correct ? | 8 Yes | 0 No |
Answer / victor edward
check for any air bubbles trapped in the impulse lines. vent
it and flush the lines. it should be solved.
Is This Answer Correct ? | 1 Yes | 1 No |
how to measure level under ground tank ? which type of transmitter very accuracy ?
What is the definition of direct acting valve & reverse acting valve
Advantages of servers over normal desktop in PLC SCADA system
How to do manual mapping in radar type level transmitter?
Relation in MMWC to Flow rate
Qatar fertilizer call me for interview as Instrumentation Project Engineer. Please let me know what kind of question they asked ? ALso they said they will take Written test, any idea about this written test ?
can i get any detail of interview question asked for instrumentation,plc,scada ,dcs..............
Explain the difference between mmwc and mmwg?
What is mean by trim?
What is difference between scada and virtual instrumentation?
I HAVE PRESSURE TRANSMITTER WITH TWO WIRES 24 VOLTS SUPPLY.IF TRANSMITTER WILL GIVE SIGNAL TO THE DCS WHAT HAPPEN TO THE 24 VOLTS POWER SUPPLY IT WILL DROP OR REMAIN TO 24 VOLTS POWER SUPPLY.
If a normal magnetic type flow transmitter that can measure flow, temperature and show this parameters on field, is it possible by any means to get this (flow and temperature) parameters info. On dcs? And if yes then with HART, FO communication or any other communication system?
1 Answers Process Control Technologies,