what is the reason for flow fluctuations happen on
differential flow transmitter during in service
Answers were Sorted based on User's Feedback
Answer / seth
Change in process pressure, restriction in one of the
sensing lines, rapid change in temperature, noise in the
signal being returned to the source of indication. (Check
for noise in the shielding-blow down sensing lines-check if
the process media is at the correct operating temp.-make
sure the equalizer valve is closed and the sensing (hi and
lo) lines are open.
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / victor edward
check for any air bubbles trapped in the impulse lines. vent
it and flush the lines. it should be solved.
| Is This Answer Correct ? | 1 Yes | 1 No |
use of split range ? where it is used ? in which control loop it is used ?
what is function of switch, and how is it work, explain with difination
1 Answers Bapco Bahrain Petroleum Company,
how to turbine speed measurement?
1 Answers Jindal Steel and Power,
In split range control, we will control 2 outputs with time interval. Eg :(with 4-20 ma signal, for 4-12 ma we are operating one control instrument like valve & for 12-20ma we are operating other control instrumet (other valve). If we get a signal of 15ma to first instrument (Valve 1), what will happened to the first valve, and if we get signal above 20 ma to 2 valve what will happened ?
can any one explain in which term we are flow flow is it volumetric r is it mass? and y
why we use npn sensor in vibration monitoring system
What is the procedure of mounting new positioner on pneumatic control valve?
What do you do as a Engineering person EPC for Sizing&Selecting Control Valve?
how can we understand about dcs "bailey infi 90 dcs system" . how its work how signal come from field how it process and how o/p creative by controller. how its cards work.the bsic principle of working of dcs
what is mean by process control?
what is the dp across a orifice plate & how much is permanent pressure across an orifice plate.
What are the error values can accepted in flow transmitter calibration?could u give any formula for this?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)