In a transformer, the hysteresis and eddy current losses
depend upon
1.load current
2.maximum flux density in core
3.type of lamination
4.supply frequency
The correct statements are
(a) 1 and 3 (b) 2 and 3
(c) 1 and 4 (d) 2 and 4
Answers were Sorted based on User's Feedback
Answer / kuldeep
hysterisis loss=f*b^1.6
eddy losses=f^2b^2t^2
so it means these losses corresponds to frequencyand
maximum flux density
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / bunny
3 & 4 as loss is directly proportional to square of f nd
thickness of lamination
Is This Answer Correct ? | 0 Yes | 0 No |