Answer / ionp
When DOL Starter is employed the motor is loaded with full
load voltage in starting, which causes high starting
current in the circuit.
Torque is proportional to square of Voltage so employing
DOL starter we achieve High Starting Torque. Which in turn
help Motor to attain its rated speed quickly.
Available Pull out Torque help load to accelerate quickly.
The starting current which can be 5 to 7 times of full load
current can be born by motor & Associated cables etc. for
few seconds during starting & does not causes any unwanted
heating & heat losses.
Hence we prefer DOL starters where high Starting Torque is
required.
On the contrary With Star-Delta starter Starting Voltage is
1/3rd of rated Voltage & Starting current is almost 3
times. This low voltage will cause insufficient torque in
starting & time taken to attain full load speed is more, in
turn more heating & losses. Also when Motor switches to
delta mode the current kick is almost 5 times the FLC, Thus
system is subjected to 2 current kicks.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / naresh
The name itself indicates direct online starters and these
starters will employed for low rating motors, because in
low rating motors the loaded torque is also low and
capacity of starting current will not be such high enough
to make severity, but the protection of motor at voltage
levels is important. DOL starter not only ensures on & off
but the magnetic opearting coil functions in proportion to
the rated voltage. at low voltage the magentic coil trips
down and at high voltages the coil gets damaged. here the
coil used is very sensitive to the voltage and hence it is
voltage protection device and the bi-metallic strip inside
starter makes it current protection device.where as mcb is
only current protection device.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / m s venkateswara rao
Normally Starters are used to reduce the starting current. But selection of the starter is based on the type of application whether starting torque is required high, medium, normal.Normally any motor during starting will take 4 to 5 times of full load current.Up to 10 Hp usually will use DOL because of motor full load current is 13 Amps and during starting will take 65 Amps as a result supply system dos not get affect. Above 10 HP usually motor full load currents are high and during starting will draw high starting current which will affect out supply system ie voltage drop, for which all associated equipment connected with the system will be affected.Usually above 10 HP motors with a application of medium torque will use star/ delta starter to reduce starting current. If the application is required high starting torque will use dol starter irrespective of the rating of the motor.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ali
i have seen many dol motors r just running on mcb without
creating any porblem for last 4-5 years dol startor are
soft stator which is manually operated suppose in an
industry to cut metals having hacksaw machine(dol motor)
which is merely operating on mcb suppose machine in ON
suddenly there is a breakdown in electrical supply & will
resume after 2 hour & operator will assume 2 hour is
sufficient time to clean the machine & these is a good time
lets take full advatage of it & he started to cleaning the
machine & forget to OFF the mcb he is cleaning & removing
burs from blade teeth suddenly suply resume 1 hour before
than the mentioned time what will happen??????????
| Is This Answer Correct ? | 1 Yes | 2 No |
What is difference between incomer & outgoing type Vaccum Circuit Breaker?
Q-1 what are the structural and operational difference between a distribution and a power transformer? Q-2 what is skew in motors? Q-3 draw equivalent circuit of transformer Q-4 explain with phasors how pf is improved with loading in induction motors Q-5 DIFFERENT METHODS OF CABLE LAYING(interviewer asked if i heard new chemical based earthing system next) Q-6 pi model of medium length trans line Q-7 v/f control?why Q-8 vacuum circuit breaker operates in?
11 kv metering is done in my factory.Meter show PF 1.000 but kvarh lag&lead show 24&94 respectively & Avg.PF is .956 .? is what i do for inproove my PF to 1.000
WHAT IS NORMAL VECTOR GROUP USED FOR DESIGNING OF TRANSFORMERS??
How can calculate the efficency of the rectifier. input 240V AC, current 5 amps,P.F 0.98, Output is 54 V DC,62.6 A.
What is the permissible value of earth resistance and as per which standard / act / rule ?
how can we calculate fault current of a line in a 6 bus syatem if the faulted line is known?
How to select cable rating for HT/LT Panels
R u say ,that is there is any flux in your room.
How good are you in resolving the commercial issues to Employer's advantage?
how to reduce earth resistance in sandy soil.
What is a differential amplifier? Also, explain cmrr.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)