Why 4ma - 20ma signal used in instrumentation??
Answers were Sorted based on User's Feedback
Answer / avinash kumar
if we consider 0-20 or any other value then we can't
differentiate that this instrument has fault or this
instrument has in its minimum position.if it indicated 0
means, it has some fault, if it indicates 4 means it is in
on state having minimum position.so by this idea we can
differentiate b/w damage instrument and the minimum
position instrument.
| Is This Answer Correct ? | 18 Yes | 5 No |
Answer / abhishek k sharma
1:-4ma - 20ma are used to ged know about the live zero
positon.it means that if we use 0ma then we cannot get
excect error as postioner do not gos negative values.
2:- also we have less chances of noise in 4ma to 20ma range
which help us to carry out calibration.
3:- it do not produces spack if we joints its (+)/(-) so
can be used in hazard conditions.
4:-it is idealy accepted for calibration of instruments by
all.
| Is This Answer Correct ? | 6 Yes | 4 No |
Answer / sreekanth
There are some Transmitters which operate from 0 to 20 MA.
But 4-20 MA is standard.
As above one of our friend told, we cannot differentiate
whether the Instrument is fault or not when we get 0 MA.
Rather than that there is one more reason. MA will be
accurate from 3 MA. But getting exact ratio between 3 to 20
MA is bit difficult. so 4-20 MA is commonly used so that 0,
25, 50, 75, 100% can be converted in to 4- 20.
| Is This Answer Correct ? | 7 Yes | 5 No |
Answer / saba anjum
we can easily find that this signal is live zero or dead
zero.
| Is This Answer Correct ? | 1 Yes | 3 No |
what is differential pressure transmitter and transducer? how to work?
what is zenier barier and what means zone 1,zone 2,and zone 3
2 Answers Bapco Bahrain Petroleum Company,
what is function of switch, and how is it work, explain with difination
0 Answers Bapco Bahrain Petroleum Company,
what are the documentation and instrument identification system used to identify the correct device to be calibrated? name atleast three.
what is start up vent valve ? why it is used in boiler?
8 Answers ACC, Bhushan Power Steel,
Why DP level transmitter preferred for closed vessels and Radar level transmitter for open tanks??
what is difference between total flow and flow rate in general ?? explain it with daily life example.
Describe how to calibrate various types of instruments and transmitters using ISA industrial consensus standard techniques.
generally transmitter power supply having some range(12v to 35v) but the out put(4-20 mA) must same for given input.If we vary the power supply voltage then output mA also to be change according to V=IR. Is there any voltage regulator in the transmitter ?
Where is the flow transmitter installed with respect to control valve, state reason.
flow transmitter formula?
0 Answers BEMCO, Siemens, Yokogawa,
types of valves
3 Answers Bindal Papers, Kuwait Oil Company,
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)