11kv alternator commissioning test?
Answers were Sorted based on User's Feedback
Answer / naveen singh
Before commissioning of alternator following electrical tests should be done on site-
(1) IR and PI of generator
(2) Winding resistance of generator
(3) IR and winding resistance for PMG and excitor field winding.
Is This Answer Correct ? | 19 Yes | 1 No |
Answer / noel
You should check that the alternator is aligned properly
with the generator motor. this should be done according to
the manufacturers specs. Rotate the alternator and check the
gap between the rotor and the stator. Also this should be
provided by the Manufacturer. Then take and IR and PI test
and record your findings. Check that the data is on the
right parameters. And also check the wirings for the CTs.
Depending if they are European or US manufactured the flow
of the current may vary a give you incorrect trips during
commissioning.
Is This Answer Correct ? | 6 Yes | 1 No |
If 100 KAV USP dedicated earth got disconnect / Cut. What will happen at load.
1 tr is equal to how many Kw .is there any specific formula for this to get the result .
13 Answers Cipla, LG, NSN,
short notes on npn & pnp transisitor..........
If u have 60KVA UPS, than tell me how systems ( computers ) u may connect?
what is difference between 2 pole structure and 4 pole structure in transformer yard
what is the difference between analog and digital signal?
in elevator industries , how to calculate the required KVA for the elevator (elevator spec- 40A module , motor of 13.5KW, 20A)
1 Answers DLF, Tata Steel Limited,
how we check vector group dyn7
why we are caling 440 volt 3 phase supply instead of 660 volt 3 phase supply? because each phase as a voltage of 220 volt. if anybody know the answer for my question please send it to my mail id. thank you.
3 Answers College School Exams Tests, Jindal Steel and Power, JIOL, NEC,
What are the solutions for avioding sulfide formation at bimetalic (Copper &Aluminium)overhead joints?
only three phases are coming in step down tranformers.how to get neutral?
what is the healthy specific gravity of lead acid battery used in DG sets ?
3 Answers Bhushan Power Steel,