why our power production in multiples of 11.
Answers were Sorted based on User's Feedback
Answer / sobhendra
FORM FACTOR OF AC IS 1.1 . ALL VALUES WE SEE ARE RMS VALUES. RMS/AVG=FORM FACTOR WHICH IS 1.1
| Is This Answer Correct ? | 9 Yes | 0 No |
Answer / u.v.v.satyanarayana
i think it's related with formfactor
| Is This Answer Correct ? | 11 Yes | 4 No |
Why is the generator rating always in kVA and motor rating in kW?
Transformer diagram mention each parts ?
What is mean by diversity Fator?
Hot Water System (HWS). Will a 30ma elcb have more nuisance tripping than 100ma elcb
what would be the earth to neutral voltage in industries? if it is not main Taine then what will happen?
is there any phase difference occurs while primary and secondary side mutual induction occurs?
How to choose size of the cable w.r.to current carrying capacity ...
which is more danjerous high voltage or high current
No load tap changing transformer working
when 20hp 3 phase motor start no load condition in star or delta connection.find current and write formula.(tariq)
a)In a 3-phase 4-wire circuit, a circuit breaker is selected to protect the circuit whose highest fault level is 6.6 MVA. Determine the required minimum breaking capacity in kA. (Note: Covert 3-phase power in terms of kA to find answer.) b)Using the below, determine the required minimum making capacity in kA as a “peak value”. Rate breaking capacity (Icn) ka: Icn<= 1.5 Factor = 1.41 1.5
Earth bits close or open. Which is correct
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)