how u measure flow?orifice measurement?why all ft in square
root?
Answer / manoj kumar
There are several ways to measure the flow of fluid & gas
like magnetic flow meter, mass flow meter, based on
measurement of differential pressure like venturi, orifice
etc, turbine flow meter, positive displacement flow meter,
vortex flow meter.
Measurement of flow with the help of orifice is based on
the measurement of differential pressure across the orifice
plate. Tappings are either on the supporting flange or at D
& D/2 m away for upstream and downstream of the orifice
respectively where D id Pipe diameter in which plate is
installed.
Not all the transmitters are square root.Those transmitters
which are based on differential pressure are square root.
We can use square root at the transmitter itself or we can
make the calculation in the DCS/PLC program.
Since Q(flow) is directly proportional to square root of
the differential pressure we do the square root extraction
to measure the flow.
| Is This Answer Correct ? | 7 Yes | 2 No |
WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?
23 Answers Exxon Mobil, Honeywell,
relation between level and differential pressure.
Good evening all I need a small favour regarding reliance paper i wanna probable sample papers(e&i) of reliance. if any of u have any idea about dis then plz mail me back.i belongs to electronics and instrumentation engg.so i need e&i papers. thanking u....
Why we use DPT? can we use PT instead of DPT?
what is the procedure of belt scale calibration?
What is the purpose of MATLAB?
T.x range -0.1 to 0.2 milibar,so how much mili ampear at 0.1 milibar?
We do have a problem in the company that is one PT connected to PlC which is mean 1 out of 1 in PLC system we do have the PAHH is 55 mbar and PALL 8 mbar with a timer of 15 sec for the PAHH the problem started when PAHH goes more than the set point which is 55 it reached up to 71 but due to timer doesn't trip . We force it and we checked everything nothing there . We replaced the transmitter problem still there the reading goes more than the 55 bar the range for transmitte is 0- 60 mbar . So we did loop check , aculaizing valve , wiring all are okay . What the possible causes for this ???
2 Answers National Petrochemical Company,
How a rtd work, and what volts/current goes to a RTD to measure the resistence?
hi sir yhis is zahid ali i am preparing for the jspl at oct.4.please send me the recently updated sample paper.
How to calibrate displacer type level transmitter (chemtrol make )for level measurement in hotwell , LP & HP heater ?
whats the problem will arrise if we rotate the hosing screw of the differential pressure transmitter?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)