1)what is hypo test. 2) which cable need to hypo test.3)
when hypo test can be done before or after glanding.4) what
is the purpose of hypo test.
Answers were Sorted based on User's Feedback
Answer / mukund
high potential test carried between line-line, line-
neurtal,line and neutral to graund on any control panelto
check insulation between live conductors and enclosure body
at hv like 1.5kv and onward depands on system voltage and
local standard, it is carried out also on control wiring too
e.g. from 300 to 600v it need 2.7kv test for 1 second and
2.4kv for 1 minuts,note when this test have to do test job
must disconnected from line voltage,it is most likely
megeer test, after testing it need to discharge tested line
to graund
Is This Answer Correct ? | 37 Yes | 7 No |
Answer / shams
hypo test is mostly used when any new cable is used or any cable which is repaired like tertiary cable in transformer.it is used to test the leakage current.20kv to 100kv dc is applied through hypo device to the testing material then the hypo device shows us the leakage current of that material
Is This Answer Correct ? | 29 Yes | 1 No |
Answer / k.prakashchandra
It is high potential test. It is done on HV cables
compulsorily.Testing after glanding is mandatory.With this
test, we may know the highest safe working voltage
Is This Answer Correct ? | 24 Yes | 7 No |
Answer / sajid
t is high potential test. It is done on HV cables
compulsorily.Testing after glanding is mandatory.With this
test, we may know the highest safe working voltage
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / muthu
hypo test meas cable strengthness cable inside armour to conductor shot have checking armour inject voltage conductor earth will check leakage current MA Formula 2E+1 ,E=Voltage 80% voltage inject
Is This Answer Correct ? | 0 Yes | 0 No |
i am iti student i have project to do. that IS 100MW 220\33KV SUBSTATION I WANT TO KNOW HOW TO START, LIKE CALCULATION, WHAT RATING OF CT,CVT, PT, ISOLATOR LIGHTING ARRESTER WAVE TRAP CIRCUIT BREAKER IN 22OKV SIDE, ALSO TO WARDS 33KV SIDE PLS HELP ME WITH THIS, THIS MY LIFE NOW, I KNOW AUTOCAD, I LIKE TO KNOW HOW TO CALCULATE ALL THE THINGS
Why do power lines not short out when they fall into water?
Does VT metering core can be used for synchronizing.
1 Answers Shrishti Power Technologies,
why earthing is not required on transformer prymary winding side ???
For 415v,3phase,22kw rating of motor how to calculate MCCB rating
What is icu and ics in Acb and how many time icu or ics passes from breaker?
Why shunt Generator is not recommended to start at ON LOAD condition???
What is the output of 25 kva 11/.4 kv transformer in kw ? Plz generalized it...
What is meant by derating factor?
what is deffrent alternatid and gernater
WHAT IS THE DIFFERENCE BETWEEN KW AND KVA ?
How to identify the whether its an isolator or Breaker in MDB