what voltage to be select in megger for insulation
resistance testing to L.V , H.T cables,motors and
transfomer?and ohms valve should be giga ohms only or what?
Answer / guest
You must know what is the voltage of your installation or
the cable. Eg. if its used for 230 v. Then you can use 250V
Megger or even 500V megger. For 440V application or cables
use 500V or 1000v megger.
For HT cables 3.3kv and above you can use 5kv megger.
Ohms value will come according to the reading. If reading
is in Megaohms or Gigaohms it will appear on the scale or
change tapping accordingly if any.
| Is This Answer Correct ? | 26 Yes | 5 No |
How to find the maximum load that can supply by a particular(say 315kva) KVA rated transformer?
what is the star delta connetion and how can do it a three phase motor with control witing with picture
0 Answers Aurobindo, SA Kent, Wipro,
FLP zone Types and Details
in telecom we are using neutral?
How to check maintenance free battery 12V,26AH using analog multimeter
what is the k var ratting of 1250kva
Whay you want to change your job.
how will be power factor while using the resistive load and Capacitive load?
what is derated current of power cable & what is formule to find derated current?
What will happen if the 50HZ Transformer is connected with 60HZ power Supply
In track electrification Either we use single conductor or double conductor? why?
why we use iron corn in transformer instead of wooden core
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)