what voltage to be select in megger for insulation
resistance testing to L.V , H.T cables,motors and
transfomer?and ohms valve should be giga ohms only or what?
Answer / guest
You must know what is the voltage of your installation or
the cable. Eg. if its used for 230 v. Then you can use 250V
Megger or even 500V megger. For 440V application or cables
use 500V or 1000v megger.
For HT cables 3.3kv and above you can use 5kv megger.
Ohms value will come according to the reading. If reading
is in Megaohms or Gigaohms it will appear on the scale or
change tapping accordingly if any.
Is This Answer Correct ? | 26 Yes | 5 No |
HOW TO CALCULATE THE SIZE OF CABLE COPPER & ALUMINIUM
11 Answers Amman Try, Prestige,
What is fault level?How it is calculated and how it is Expressed?
In 11/0.414 KV Parralel supply network with Bus tie closed what will be the fault level is it doubled or halved??
how to test generator protection rotor earth fault relay and locked rotor test?
which motors are used in electric traction?
If a motor of 8.5 KW with same load and using in both Star & Delta one by one,then which will take more current in star connected or in delta connected
5.WHICH TYPE WELDING PROCESSES USES NON CONSUMABLE ELECTRODE.........
oil sample dielectric test gives the insulation rupture voltage at 26 kv. is this transformer safe to be operated . The working voltage is 11 kv
can we start a 6.6kv ht motor with 415 lt supply
How can transformer oil be used in transformers with voltage rating above its breakdown voltage?
why we are giving D.C. supply to field of an alternator, why can't we give the a.C. supply
what is size of 3phase 4wire cable to be used for 11 ton ductable A.C and how to calculate cable size for different load