What is passive connection of instrument in different type
of I/O module
What is passive connection of instrument in different type of I/O module?
What is passive connection of instrument in different type of I/O module?
The output of a field instrument or analyzer that makes a measurement and provides a conditioned, high level signal like 4-20mA is characterized as either active or passive.
An active output is powered internally by the instrument. These are 3 or 4 wire instruments with a separate power wire or wires.
A passive output requires a DC power supply in series with its output in order to excite or power the output. This done to
- limit field wiring to 2 wires
- reduce the likelihood of a ground loop due to difference in ground potential between the field instrument and the receiver.
So, a connection of a passive (2 wire, loop powered) device has to include connections to a DC power supply, observing correct polarity at the field device and the receiver's analog input.
Carl Ellis
Measure First
| Is This Answer Correct ? | 0 Yes | 0 No |
why we used for range in pnumatic 3-15 psi and current 4-20 ma?
detail of mass flow meter pricipal
Describe the function of Accumulator into the Pump
what is skin type thermocouple? how it is installed? what is the difference b/w thermocouple & skin type thermocouple? what is gounded & non-grounded thermocoplle? what is the diff b/w these two?
2 Answers KazStroy Engineering, PSU,
why 4 to 20 ma ,why not 0 to 20 or 3 to 15 or anything
19 Answers Honeywell, TCS, TN,
If an Instrument has 550 ohm internal resistance and the cable used for that instrument is 0.5 ohm per meter resistance. If the voltage is 12volt.How much length cable can be used?
How to check the SCAN time of DCS ,n dont give therotical answers .How to check the SCAN time of DCS during FAT?
what is difference between differial pressure & delta pressure?
what is the Instrumentation?
what is flow equation of kg/hr to m3/hr
draw the block diagram of a level transmitter ?
0 Answers Hira Group, Samsung,
If boiler drum level transmitter is not working properly what you will do for resolving the problem in plant running condition?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)