What are the components ofan HT panel in a 11kv power
station?
Answers were Sorted based on User's Feedback
Answer / manoj
The HT panel is the front side (usually) of HT cubicle. If
it is a local control panel there will be one alarm
annunciator ,meters for the indication of different
parameters of electricity ,normal control push
buttons,emergency control push buttons,bypass key for all
interlocks,"local,remote or maintenance" selector rotary
switch,semaphore indicators for CB/isolator/earthing
switch,push button for healthy checks of tripping coils
(before closing and after closing).There wiil be no
hazardous HT voltages as the name indicates,only control
power(110 dc,110 ac,240v ac,440v ac).Inside the cubicle
there will be ,space heater,resistances,fuses,SMPS power
supplies auxiliary relays(protection panel) etc.
| Is This Answer Correct ? | 21 Yes | 6 No |
Why is DC use instead of AC for protection and control circuits?
What is hysteresis loss?
what is meant by AYFY Cable?
is it value of power factor is more than unit. whats effects in the source supply
why we setting 95 deg and 105 deg in wti and oti of distibution transformer ? give the reson for that ?
You are of electrical field and you are going for software? Why
How to calculate the input cable rating for 10kva ups (3phase input and single phase output and also 3phase output, battery rating 65Ah)provide the formula also.thnx
Why Earth pits are inter connected
what is the effect of un-synchronized power.
what is meaning volt-hz ration,where is necessry tomaintain and why. specialy during increase the power of generator.
234 MVA Generator 3 phase Short circuit current Values required? Gen set Rating-234 MVA, Gen Voltage-18kv, PF;0.8, Xdv:23.5 %, Transformer Rating-18/380KV, 680MVA,Yndd1 two winding, Step up TR, ZT:35.50 %,X/R 4.33 Gen CB Position, CB open ,Disconnected open, Generator Running Voltage 18 Kv, Bi mistakes generator side earth switch Closed during that time short circuit current level in 3 Phase required, and how to test on site 234MVA Generator Short circuit current,
What is the current carring capacity of 0000SWG and 0SWG overhead solid bare copper conductor. If possible please provide reference for various sizes Vs current ratings
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)