fault level depends on your system's percetage impedance.In
general practice we are using 28KA for 3 secs. or 40KA for
3 secs.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / genau
Mr. Ranjan is correct!!
Fault level of the system will depend on the system impedance.
for calculation of fault level, calculate the fault impedance and hence you can calculate fault current from system voltage and fault impedance. product of two gives fault level in VA (Generally specified in MVA)
Is This Answer Correct ? | 0 Yes | 0 No |
how brushed dc motor operating ?
how to test the turn ratio of 3 phase transformer using volt meter shoe the curcit diagram.
Why transformer, generator, ups rating kva?
how induction generator generated the power without excition like syncronous generator.
What are the advantages and disadvantages of short-pitched winding?
Good morning: I'm looking for some informations about the OLTC or the LTC: I wont to know what the function of the tie-resistor in during the operation of reversing/coarse operation Cordially
can any one know is sbi interview based on merit or based on roll number
What is the difference between AC Drives and DC Drives?
14 Answers College School Exams Tests, La-Gajjar Machineries, LG, Schneider, SMEL,
How to calculate size of HT breaker with the help of Amp (current)? Please provide answers with examples.
HOW TO CALCULATE GROUND FAULT CURRENT IN 430V 4000AMP AIR CIRCUIT BREAKER?
transformer is connected with 50hz and 60hz at same rating which will give more output on same rating
how to enter inverter parameter? without manaual?