What is mean by earthed & unearthed cable? Voltage grade of
1.9/3.3 kV(E), 3.3/3.3 kV(UE), 3.8/6.6 kV(E)what it
indicates??
Answers were Sorted based on User's Feedback
Answer / ganeesh jain
There are earthed and unearthed cables for earthed and unearthed systems respectively.
Here, 1.9/3.3 kV = Uo/U = Phase to Earth Volt / Phase to Phase
1.9 X 1.732 = 3.3
Previously our systems were of small ratings and hence the short circuit faults were less and therefore lesser insulations were required for conductor. Whereas in advancement of time in modular system, huge fault currents are present and hence the insulation level on cables.
In earthed systems, Phase to earth voltage is 1.732 times the phase to phase voltage, where as in unearthed systems, phase to earth voltage can be equal to phase to phase voltage.
Therefore in earthed system ,stress on conductor to armour is 1.732 times lesser than the stress on conductor to conductor and hence lesser insulation is required between conductor and armour while in unearthed systems, since Ph-Earth voltage can be same as that of Ph-Ph voltage therefore the stress between conductor and armour will be more and hence the insulation.
Therefore manufacturers have designed 3 insulation classes for cables as per system design.
Insulation Class:
1. 100% : For solidly earthed systems, or on any system where the protective device will clear earth faults within 1 minute.
2. 133% : For systems where the protective device is expected to clear earth faults within 1 hour, and is typically specified for high impedance earthed or unearthed systems.
3. 173% : For systems where the time to clear an earth fault is indefinite. This is typically recommended for unearthed or resonant earthed systems.
In simple logic the 11 KV earthed cable is suitable for use in 6.6 KV unearthed system. The process of manufacture of cable is same. The size of cable will depend on current rating and voltage level.
Voltage Grade (Uo/U) where Uo is Phase to Earth Voltage & U is Phase to Phase Voltage.
Earthed system has insulation grade of KV / 1.75 x KV.
For Earthed System (Uo/U): 1.9/3.3 kV, 3.8/6.6 kV, 6.35/11 kV, 12.7/22 kV and 19/33 kV.
Unearthed system has insulation grade of KV / KV.
For Unearthed System (Uo/U): 3.3/3.3 kV and 11/11 kV.
3 phase 3 wire system has normally Unearthed grade cables and 3 phase 4 wire systems can be used earthed grade cables, insulation used is less, and cost is less.
Is This Answer Correct ? | 9 Yes | 0 No |
The metal sheath is earthed or unearthed. 1.9/3.3 and
3.8/6.6 are phase/ line voltages and are 3 core
cables.3.3/3.3 KV means 2 core cable for single phase
supply ,as neutral is present earthing is not necessary.UE
means unearthed E means earthed
Is This Answer Correct ? | 14 Yes | 9 No |
Why do we mix soda with water in LRS?
define transient state &steady state
What is eddy current & eddy current loss ?
What are the causes of electrical faults?
What are the complete specifications of a motor?.
What is The Resistance Formula
please suggest some good universities with low cost iam in totally full confusion so please help me my profile gre 283 and ielts 5.5
What is the function of the auto reclosure relay?
Cables Construction hi friends, 0.6/1/1.2 kV LV , DC and Control cables are concentric copper conductor what does its means and what is the use of concentric copper conductor,and are this with copper tape shield or copper screening, ? thanks
If AVR fails in DG set what will be the affect?
17 Answers GoodYear, Hotline Glass, HSL,
WHAT IS THE DIFFERENCE BETWEEN NEUTRAL AND EARTHING
1 Answers Adani, Adani Power, Raychem RPG,
What does OHB stand for in specifications for circuit breakers, especially found in SF6 circuit breaker?