how much load 15kva dg set can bear.with full explination
and how to calculate?
Answers were Sorted based on User's Feedback
Answer / amit chaudhary
The full load of 15 Kva DG set will be 12 KW on 0.8 power
factor. if the DG set is 3 phase(415 v) then per phase
current will be I = 15000/(1.732X 415)= 20.86Amp/PHASE
Is This Answer Correct ? | 28 Yes | 8 No |