what is the role of impedance in transformer?based on
secondary f.l.current(139 amps) and impedance(4.07) of
415/415v of 100 kva transformer. what is the primary
current?
Answer / ma.amulraaj,b.e. mba.,
It is %impedance Voltage.In Transformer,%impedance Voltage plays significant role .Here 100KVA,11KV /415 V.
Full load current Sec .current= VA / 1.732x V (Sec.Voltage)
=(100x 1000 )/(1.732x415 ) =139 Amps, ok
Full load current Primary .current= VA / 1.732x V (Primary
Voltage)
=(100 x 1000)/(1.732 x 11000)
=5.25 Amps
Here ,the full load secondary current is 139 Amps,the rated secondary voltage is 415 V,we can do Short circuit test by applying secondary voltage 415 V,we cannot get the full load secondary current,due to impedance of Transformer.Then we have to raise the secondary voltage gradually, at particular voltage it delivered the full load secondary current,note down the voltage say 440V.From that voltage we have to find out % impedance.440 /11000 = 4% %Z=4.0 %.As this case %Z=4.07,ie. it is (4.07 x11000)/100 =447.7 V.It means This transformer may delivered a full load current at 447V.
This % Impedance may vary from Transformer to Transformer.
| Is This Answer Correct ? | 3 Yes | 1 No |
What is the List of Equipments, Instruments, Components required in Transmission of electricity from 1 substation to other substation(The equipments required in substation too)? What are the differnt IS standrds used for above equipments in Industry?
WHAT IS DIFFERENCE BETWEEN idmt and instentanous relay? is idmt is used as back up protection or else?or when instantenous relay saturates IDMT will operate???
basic of electrical information where i can get? plz send the website which you know?
What are the site acceptance tests for power cables, DG Sets, LT panels & 30kVA UPS ?
what are the industrail measures to over ferranti effect? how would the ferranti effect the power system if those remedial mearsure arent taken? how often does this effect occurs in real power system?
what is the difference between electrical & electronics?
why neutral used in three phase motor connection?
What are the possible causes of REF operation on a power transformer
how i caculate the cable size for power factor correction unit for example 300kvar
(1)WHAT HAPPENS WHEN SUDDENLY LOAD GIVEN TO THE INDUCTION MOTOR ? (2)CAN WE MAKE WOOD AS MAGNET ? (3)WHAT IS THE VALUE OF MAGNETIC FLUX DENSITY IN TRANSFORMER ? (4)WHY WE ARE USING ELECTROMAGNETI NOT ELECTROSTATIC IN MACHINE ?
what is the need of reactor in between the transmission line?..like powergrid like that..
Why arc quenching is used in Diode ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)