why neutral grounding transformer is used for generator and
why it is not used for transformers?
Answers were Sorted based on User's Feedback
Answer / tanvir s.
As far as i understand Neutral Grounding Transformer are used to Ground the both transformers as well as Generators. NGT is applicable (useful) in transformers/generators with delta connection. So during line-to-earth faults, the NGT helps the zero sequence current to flow in the ground. Any unbalance in the load distribution between the three phases is passed thru the neutral, which is not available in case of delta connection. Hence the NGT.
| Is This Answer Correct ? | 9 Yes | 4 No |
Answer / sunil kumar sinha
Neutral grounding transformer is used to limit earthfault
currentof generator. It also provide Generator earthfault
protection, both alarm and trippingby connecting voltage
relay across the secondary winding of NGT.
| Is This Answer Correct ? | 4 Yes | 1 No |
1.what is the difference between ct and cvt? 2.what is the difference between pt and cvt? 3.what is the difference between relays and circuit breakers?
what is the difference in inductance and resistance.both oppose the flow of current but how.resistance having + ve power in both cycle while inductance having both power.
What is Star Delta Connection, where it is applied & what for it is used
4 Answers Premium Transmission,
why various test are performed on electrical panels & power cables before commissioning on site & what are these test???
why transmission line towers are longer than communication line towers?
why abcd parameters are called transmission parameters
How can I calculate the require lumen of a room. If I use Tube Light (40 W), Or 100 W incandescent lamp. Please give detail answer.
what is the function of starter & choke in the tube light set & how choke give 1000 volts while switching on.
14 Answers ADNOC Abu Dhabi National Oil Company, IBM,
Dear sir, I completed DECE In the year 1995.Now i am working in a private company from last 10 years as an Electrical supervisor.The company having a 1000 KVA transformer.Now i try to apply "C" Licence. I am eligible or not.If not eligible,pls give solution.
ASTM D 3455 - Standard Test Methods for Compatibility of Construction Material with Electrical Insulating Oil of Petroleum Origin has been used for Testing Transformer Oils with a product placed in it. Aged Control Oil has a Power Factor of 0.032% at 100°C. Aged Oil with a Test component has a Power Factor of 0.093% at 100°. Is this increase acceptable? If not why? How much increase is acceptable?
What is the difference between KV,KVAR,KVA,KW?
6 Answers L&T, PowerHouse, YUI,
HOW TO CALCULATE THE HEAT AND LOAD OF LT-SUBSTATION WHICH CONTAINS 2*1MVA TRANSFORMERS,LT-SWITCH BOARD,MLDB,ACB,BUSBAR,ETC,......?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)