What kinds of decision are made about CT from it's Knee
point(voltage & current)?
Answers were Sorted based on User's Feedback
Answer / shariff
Knee Point Vog is the Point where the Votlatge shouts up
and the Current gets saturated for the CT across its cors
and it is a very vital parameter for any current
transformer. And this Knee Voltage value should be same for
all the 3 phases of the CT.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / raj
For Protection CTs knee point voltage is always high than
Metering CTs to avoid saturation of CTs during fault
current.But to increase the knee voltage core size should
be increase which is practically possible or economical so
another method to reduce the burden on CTs by using
secondary ratio 1A inplace of 5A.
| Is This Answer Correct ? | 1 Yes | 0 No |
why lightning arrester and other equipment earthing conneting from same earth bar ?
any idea abt REVERSE METERING concept.........?
is it possible to say motor horsepower number without seeing name plate(when name plate damaged)
which is the best institute for PLC,SCADA,DCS in hyderabad
i need to calculate high voltage line power factor daily basics but there is meter reading kwh and kvah while calculating power factor kwh/kvah formula was right. for examble there is point c=13kwh c=1.8 lag c=1.2 lead and c=14.5kvah like that i know that p.f =kwh/kvah but c=1.8lag kvarh and c=1.2lead kvarh points i dont know if u know please reply
How to calibrate or test an LT Air Circuit breaker 440 volts, 35 KA, 800 Amps ?
What is the difference between earth fault protection of motor feeder with CBCT and Without CBCT ?
0 Answers Enmas, Michelin, Reliance,
Where we can use 3.5c cables instead of 4c cables.Why?
any body,pls tell me how to done relay coordination ? how to coordinate by TCC curve?how to read the tcc curve?
A 3PH MOTOR RUNNING IN NORMAL CONDITION AND ITS AMPERE ALSO UNDER ITS FULL LOAD CURRENT,ITS CABLE RATINGS ALSO HIGER THN ITS CAPACITY,BUT ITS CABLE GETTING ABNORMAL HEAT(NOT TOO HOT)WHY ITS GETTING HOT LIK THIS
Why two main buses and one transfer bus scheme not using for 400kV switchyard
Why restricted earth fault protection is needed? Why can’t differential Protection is sufficient?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)