1,why we use 4-20 ma output of all instrument qhy not use 0-
20,
2,what is the different between PLC & DCS.
3,how can we meaure maximum span of new flowmeter if not
given any information.

Answers were Sorted based on User's Feedback



1,why we use 4-20 ma output of all instrument qhy not use 0- 20, 2,what is the different between P..

Answer / rohan g

0 to 20 vdc signal may detoriate over distance but current
signal will remain intact.
noise will not affect current signal at all but vdc signal
will get affected.
if equipment fails then also it gives 0 vdc signal in case
of 1 to 20 vdc.but not in case of 4 to 20 ma.
DCS can be viwed as bigger version of PLC.Since no i/p dcs
can support is more in case of dcs.Also dcs can have
operator interface but plc dosent have such.

Is This Answer Correct ?    17 Yes 5 No

1,why we use 4-20 ma output of all instrument qhy not use 0- 20, 2,what is the different between P..

Answer / narendra mishra

suppose 0 to 20ma is used where 0 for
min.process value and 20 for max.then if
feed back cable get shorten or erthed or
broken it wil show min process value.where
in case of 4 to 20ma it will show "bad".

Plc are used to handle specific area where
DI DO signals are required like burner
managment system.plc response time is in
milisec. And that of dcs is in microsec.

Max span can be found by taking it online
and interfacing it with HART.

Is This Answer Correct ?    13 Yes 4 No

1,why we use 4-20 ma output of all instrument qhy not use 0- 20, 2,what is the different between P..

Answer / himanshu apte

4-20 mA current has the highest linearity with the field
instruments. Same linearity cannot be found in other
current options like 0-20mA or any others. In addition to
that, a cable failure in case of 0-20mA will not be
detected if the signal is already at 0 mA.

PLC have a very small scan time i.e. @ 50-100 milliseconds,
which is useful in Emergency shutdown systems..Controlling
algorithms are available in modern PLCs, but fine tuning of
controllers can be better achieved with DCS. DCS has a scan
time in the range @ 500ms, which is why it cannot be used
in ESD systems. DCS can also handle more no. of I/Os than
PLC.

Is This Answer Correct ?    3 Yes 2 No

1,why we use 4-20 ma output of all instrument qhy not use 0- 20, 2,what is the different between P..

Answer / samir

4-20 ma is used to instrument because if there is an
instrument faulty of it not getting the power or damage then
it gives 0 ma signal so we can found that the instrument is
faulty so we can easily check the instrument.
if we use 0- 20 ma we can not identify from the signal that
the instruments is faulty or actual the low signal from the
instrument during the measurement.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

what is difference between two wire &three wire pt 100 ?

3 Answers   Jindal,


Rtd sensor how to calibrate

5 Answers   Sepam Group,


TECHNICAL/ARTITUDE

0 Answers   ONGC,


what is absolute pressure, gauge pressure and atmospheric pressure?

2 Answers   Mother Dairy,


How many loops are there in the power plant? how many closed & open loop in the power plant ? Please give me the exact clarification?

2 Answers   Lanco, Reliance,






suppose in dcs range of a flow transmitter is 10t/hr what is dp for 50% in 2500mmwc

6 Answers   Chevron,


generally transmitter power supply having some range(12v to 35v) but the out put(4-20 mA) must same for given input.If we vary the power supply voltage then output mA also to be change according to V=IR. Is there any voltage regulator in the transmitter ?

1 Answers   Indian Steel,


what different types of problems do occur while doing instrumentation commisioning and how to solve them? please explain in detail

0 Answers   Process Control Technologies,


Sir, I am working as a Instrument Engineer in Grasim Industries. Can any body provide question answer for interview purpose

0 Answers   Grasim,


this site is owned by an nonsense

0 Answers   Bhel, Prolific,


why the supply frequency used in America is 60Hz while that used in India is 50Hz?,

2 Answers   Bosch, Genco,


Transducer Input 0 to 230 v ac Output-0 to 10vdc Receiver Input 0 to 10 vdc and Output 4 to 20 ma How?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)