WHAT SHOULD BE THE RATING OF MCCB FOR 415V,3Ph,50KVAR
CAPACITOR BANK
Answer / vijay kumar
The capacitor current would be kvar x 1000 / (415 x sqrt3). This would be 70a approx. The MCCB selected should have atleast 1.4 times this current i.e. 1.4 x 70= 98. So you should choose at least 100 A mccb.
| Is This Answer Correct ? | 3 Yes | 0 No |
What are effect of radio system in DCS Distributed control system ?
WHAT IS SHORT CIRCUIT STRENGTH OF 100 AMPS MCCB?
Is there any other method of damping the oscillation in a synchronous motor other than using damper winding and if yes what is it?
Can anybody explain Why starters are not used for motor starting in industries?
How can we design MEP services for Commercial Building in area about 22 Acres of land?
how snubber circuit works to protect switching devices?
What are the protections required in the main lt panel which is connected to the transformer.
WHY TRANSFORMERS ARE RATED IN 11KV 22KV 33KV Instead off 10kv 20kv 30kv
what is the difference between online and offline UPS?
what is dc system? how getting pulse from rectifier?
if z transform lies in ROC then. a)system is stable b)inverse of system is stable c)both system and its inverse are stable.
What are IR values and what it should be for coil and for insulator
0 Answers GPSC Gujarat Public Service Commission,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)