What should be the DC voltage for Hi-pot test on 11kv switchgear
Answers were Sorted based on User's Feedback
Answer / gunasekaran
calculation is (2E+1)1.414
(11*2+1)1.414=23*1.414=32.52*.85=28kV already HV test done
at factory so we have applie only 85%of rated voltage
| Is This Answer Correct ? | 12 Yes | 5 No |
Answer / solanki
i think it will be the around 23 kv for the 11 kv switchgear
bcz its take the calculation twice of rated switchgear voltage
| Is This Answer Correct ? | 4 Yes | 9 No |
Why generating voltage is limited up to 22kV?
What are the disadvantges of leading power factor
what is the difference between power transformer & distribution transformer and what are their ratings respectively?
What is a copper loss or i2r loss pc?
what is the use of sdf?
What it indicates by 25/41MVA on transformer?
what modulation is used in landline telephone signals?
how do you measure earth leakages in 3phase wires?
why we calculate only 11kv 33kv and 132kv ... why not 10kv 20kv 45kv?
What is the difference between type1 and type2 relay protection co-ordination for motor feeders
What are the basic elements used for modeling mechanical rotational system?
why tertiary winding is used in transformer with diagram?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)