What should be the DC voltage for Hi-pot test on 11kv switchgear
Answers were Sorted based on User's Feedback
Answer / gunasekaran
calculation is (2E+1)1.414
(11*2+1)1.414=23*1.414=32.52*.85=28kV already HV test done
at factory so we have applie only 85%of rated voltage
| Is This Answer Correct ? | 12 Yes | 5 No |
Answer / solanki
i think it will be the around 23 kv for the 11 kv switchgear
bcz its take the calculation twice of rated switchgear voltage
| Is This Answer Correct ? | 4 Yes | 9 No |
I meggared my 2c*70 sq mm AL AR XLPE cable. its one end show 50 M ohm . is my cable is safe for laying. I have only one phase and neutral.
Why not using Air circuit breaker at High tension side?
In IDMT RELAY the term minimum (M) indicates what?
in dc machine airgap is there b\w stator and armature but by conduction emf is generated how & what is conduction
what is the difference between UPS & Inverter
How to calculate the current capacity of the 3C / 1C Al/Cu power cable???
The safest value of current which can pass from human body?
why the tapping of transformer on ht side??????
12 Answers CTS, OPTCL, Visa Steel,
if the HR asked to me., you have got 92% in higher secondary but got only 72% in engg whats the reason??what should i have to say ..please help me..
Sir, plz tell me how droop setting is done in parellel operation od DG set ? please give practical example ?
why h parameter are called as hybrid parameter?
What do you mean by ACB and VCB?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)