Two alternators say 1 & 2 are poised to parallel operation.
But at the time of paralleing alternator 2 gets out of the
system by tripping Earth fault relay. Please send me reply
why this is happening?
Answers were Sorted based on User's Feedback
Answer / jyotirmoy das gupta
The answer depends on the following parameters: 1. At which
point the two generating systems are earthed, 2. Is there a
neutral isolation for the second generator, 3. how the
earth fault sensing element is connected- by 3 phase CT
forming residual circuit or direct measurement placing the
CT between generator star point and earth, 4. what is the %
setting for earth fault protection and what delay is
setted.
| Is This Answer Correct ? | 3 Yes | 1 No |
In addition to the above answer, what type of earthing is
provided for both the generators also matters. Secondly, if
it is NGR, which NGR is closed, or both are closed.
| Is This Answer Correct ? | 1 Yes | 0 No |
In tranformer winding Connection Like Dyn1 ,so LV lags Hv by 30 deg and Dyn11 LV lead HV by 30,so how do this lagging and leading afffect the transformer??
what is the formula of knowing the clabe size on any load?
What causal system?
What is deference between MCB & MCCB & ISOLATOR
0 Answers Prakash Industries, Standard Chartered,
What is electrical energy ,power?
Explain M Var? Which types of problem occurs when reactive power increase at the time of full load of plant and at the time of synchronize of plant?
why overload relay is not tripped at time of starting of motor allthough staring current is too high?
if a 2 ohm resistor,2 ohm capacitor and a 2 ohm inductor is connected parallely to 12v source.Then what is the value of current in each branch.Is current flows in each branch at the same time?If not so then provide the proper sequence
as ac supply is given 2 the transformer why it doesnot depends upon powerfactor????
What will happen to the protection and metering, if the polarity of a single or two PT/PTs in three phase system is reversed? Please provide reference if any.
What fomula is used to calculate: 1. rated frequency withstand voltage, and 2. rated lightning impulse withstand voltage.
what's the requirement of Dy11d0 connection of 3 phase transformer?what's use of it?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)