voltage of a ckt is measured by volt meter having an input
impedence camparable with the out put impedance of the ckt
Eror caused is
1. Gross Error
2. Errors due to lloading effect
Answers were Sorted based on User's Feedback
Answer / sandeep
though it seems errors is due to loading effect, it can be
Gross error also a it is misuse of the instrument. please
justify..
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / hrs
It is due to loading effect..if load is not connected to ckt
then current will not flow through it so input impedance
will not come in picture...
| Is This Answer Correct ? | 0 Yes | 0 No |
i am working in automation feild my question is that how to find the KVA of transformer.
DERIVE AN EXPREION FOR MAXIMUM POER TRANSMISSION, WHAT ARE ITS APPLICATIONS.
can v rotate single phase induction motor in both the direction...?
what is the main difference b/w contactor and relay
2 Answers Pace Pharmaceuticals,
what is the breakdown voltage value in BDV test in transformers?
How can you measure the signal from the PT100 sensor?
comparision between ACB and VCB
What will happen if I apply DC to AC transformer? please send detailed answer at habib_rahman_habib786@yahoo.com
why do you want leave the company
why wire sizes are 3/29 or 7/29 and why not wire sizes are 2/29 or 6/29?
We are having Chemical earthing pit the voltage between neutral to earth showing 22V how to solve that
What are the internal and external faults?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)