Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how can we calibrate the differential pressure transmitter
by using HART communicator

Answers were Sorted based on User's Feedback



how can we calibrate the differential pressure transmitter by using HART communicator..

Answer / guest

Probably HART communicator used for online & onfield
calibration.As per my experience,I always used to do
calibration by step given bellow:
1.First,put transmitter loop in CAL mode.In CAL mode
controller the hold last PV for reference.causes without
stop or disturb process we can do calibration earlier
(depends on process)
2.Connect HART to the transmitter +ve & -ve
terminal.observed parameter on HART
display.e.g.pressure,dp,current output singnal.& note down.
3.Then close the isolation valve of both HP & LP tapping &
loose the both HP & LP side vent plug.In this condition
transmitter shoud show zero dp because same atmospheric
pressure actig both side.If transmitter showing zero dp
transmitter is normal & If it is not showing zero,then
there is some error in dp.
4.If transimtter showing error in dp then on HART go to
diagnosis-calibration-sensor calibration-dp trim.enter the
zero dp at atmospheric condition and come back on basic
setup display,transmitter will showing 4 mA current
output.means calibration is ok.then u can take transmitter
on line.and don't forget to checked leakage from impulse
tubing & vent plug.

Another procedure is Bench calibration.Using pressure &
calibrator we can check transmitter.even without HART we
can do bench calibration.

Is This Answer Correct ?    45 Yes 2 No

how can we calibrate the differential pressure transmitter by using HART communicator..

Answer / swapnil dhamanse

Probably HART communicator used for online & onfield
calibration.As per my experience,I always used to do
calibration by step given bellow:
1.First,put transmitter loop in CAL mode.In CAL mode
controller the hold last PV for reference.causes without
stop or disturb process we can do calibration earlier
(depends on process)
2.Connect HART to the transmitter +ve & -ve
terminal.observed parameter on HART
display.e.g.pressure,dp,current output singnal.& note down.
3.Then close the isolation valve of both HP & LP tapping &
loose the both HP & LP side vent plug.In this condition
transmitter shoud show zero dp because same atmospheric
pressure acting both side.If transmitter showing zero dp
transmitter is normal & If it is not showing zero,then
there is some error in dp.
4.If transimtter showing error in dp then on HART go to
diagnosis-calibration-sensor calibration-dp trim.enter the
zero dp at atmospheric condition and come back on basic
setup display,transmitter will showing 4 mA current
output.means calibration is ok.then u can take transmitter
on line.and don't forget to checked leakage from impulse
tubing & vent plug.

Another procedure is Bench calibration.Using pressure &
calibrator we can check transmitter.even without HART we
can do bench calibration.

Is This Answer Correct ?    10 Yes 2 No

how can we calibrate the differential pressure transmitter by using HART communicator..

Answer / deepak kumar

for DPT calibration on the field :
1.at first go the field and check our tag number to which u calibrate
2.then first close the both HP & HP side isolation valve,open the equaliser valve
3.open the vent valve
(for zero triming there is pressure flow)
4.then connect the HART communicator at ve and -ve terminal
5.open the hart =>>device setup=>>diagnosis=>>calibration=>>sensor calibration =>>dp trim=>>then enter Zero trim at atmospheric pressure
(that solve)
NOTE:-after complete the calibration close it to it's normal conditions..
.
thanx...

Is This Answer Correct ?    7 Yes 0 No

how can we calibrate the differential pressure transmitter by using HART communicator..

Answer / venkatesh

First do the 0 trime and span trim, In this it self problem
will solve....ealse use hand pump in point(In HP or LP side
it's deponds up on the usage) applay the pressure check the
reading

Is This Answer Correct ?    15 Yes 9 No

how can we calibrate the differential pressure transmitter by using HART communicator..

Answer / guest

ICON CONTROLS PVT. LTD.

Is This Answer Correct ?    10 Yes 6 No

how can we calibrate the differential pressure transmitter by using HART communicator..

Answer / malchom

You can not accurately calibrate a differential pressure transmitter with a HART communicator. A communicator is just that. A communicator, not a calibrator. The communicator is displaying to the user the pressure input and ma output units that the transmitter "thinks" it is seeing and sending. These values may be quite different than the actual values being applied and sent as indicated by pressure and current calibrators which have themselves been calibrated using a known standard. You can use the communicator to adjust the transmitter to then match your calibration equipment.

Is This Answer Correct ?    3 Yes 0 No

how can we calibrate the differential pressure transmitter by using HART communicator..

Answer / vimalraj

Hart communicator is a hart of DPT Transmitter.is not a calibirator .only we connect and see the pressure , range ,MA,%., units.and also we can modified the configuration of transmitter in online mode. if any major problem for a transmitter only we do that bench calibiration using by DRUK Calibirator or handpumb

Is This Answer Correct ?    1 Yes 0 No

how can we calibrate the differential pressure transmitter by using HART communicator..

Answer / praful lilhare

first of all connect the 250 ohm resistence in series while
connecting the HART to DPT for communication tnen close all
tabs and adjust zero.we can also adjust the range,unit by
using HART communicator.

Is This Answer Correct ?    6 Yes 6 No

Post New Answer

More Instrumentation Interview Questions

Coriolis flow meter coil supply is 24vdc but why still we given 230ac for this transmitter let me explained detailed review please

1 Answers   Shell,


I am a instrument technician. recently i attend interview and face one of question for DP transmitter ,the client asking about the calibration of DP transmitter ,am answer the calibration procedure, they will ask one more question. why open LP side in atmosphere? i did not answer that question. so please help me and explain the particular question. Dear firends waiting for your valuable replay

3 Answers   Qatar Petroleums, Samsung,


How d.p. Transmitter can be applied to open tank?

0 Answers  


What is meant by cold float of compressor shaft.

1 Answers   Sabic,


what deference between panel earth and systemearth

0 Answers   Tecnimont,


Why drum level range is given -500 to 0 mmwc pls give me that answer

1 Answers  


Please can anybody tell me the step by step procedure for calibrating the Pr,Lvl,Fl,Temp transmitter on process?

1 Answers  


what is the input of digital RPM indicator during the calibration time?

1 Answers  


In your own words, would you expect an ultrasonic level device to work better in a pressure vessel with a high pressure or a strong vacuum, and why?

1 Answers  


cascade controller is feed back or feed forward or both

4 Answers  


Which type of diagphram use in costic line,DM water line,natural gas line,oil line?

0 Answers   Hindustan Zinc,


Why we use negetive (-)voltage in vibration system

4 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)