What is a PID controller and how can it to applied to our
everyday life?
Answers were Sorted based on User's Feedback
Answer / waqas ali
A PID controller is composed of three components:
P - Proportional
I - Integral
D - Differential
It controls the overall response of a system. The "P" term
controls the gain of the system. The "I" term controls
error and "D" term controls the overshoot of the system.
| Is This Answer Correct ? | 28 Yes | 3 No |
Answer / www.islamqa.com
Actually we can make it simple:
# P:
it's a controller gain which modify the controller o/p
proportional to the error.
# I:
it's a controller gain which modify the controller o/p
proportional to the integral of the error.
# D:
it's a controller gain which modify the controller o/p
proportional to error rate of change.
We have 4 parameters in our control loop to focus on:
1 - the rise time: the period of time during which the pv
get 90% of the desired sp value
2 - max overshoot
3 - settling time: the period of time during which the pv
get the desired sp value and saturate.
4 - error/offset
we can get it clear from this pic:
http://controls.ame.nd.edu/ame437/S2003/hw1/specifications.j
pg
Now we will take a look about the effect of each controller
gain on these parameters:
# P gain:
decrease rise time
increase max.overshoot
increase settling time
decrease error (but not eliminate)
# I gain:
decrease rise time
increase max.overshoot
increase settling time
eliminate error.
# D gain:
no effect on rise time
decrease max.overshoot
decrease settling time
decrease error.
the previous is guidelines to be in background while
dealing with PID,but they are not sharp limits.
Regards,
Ahmed Sabry
Control and Instrumentation Engineer
GPC - General Petroleum Company
ahmedsabry.online@gmail.com
CELL.: 00 2 0121367310
| Is This Answer Correct ? | 11 Yes | 0 No |
Answer / ajith294
At first you should understand what is the controller.
A controller is the device in a closed loop, that compares the measured valve (actual valve) with the desired valve and calculate the out put manipulated variable. Then The time (T) responds is determined by P,I,D
P: manipulated variable our put is proportional to the system deviation. that means variable only present if there is any system deviation.
I: manipulated variable is continues to increase, the system deviation decreases. this process continuous until system deviation is zero.
D: Differential compound evaluate the speed of change of the system deviation.
so if using the PID controls, we can control the flow to our desired valve at a very short time.
Best Regards
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / basheeruddin
PID controller is use to correct the errors between measure value PV ( i.e process value ) and set piont (sp).
| Is This Answer Correct ? | 4 Yes | 1 No |
in which mode of the zener diode act when load voltage is approximately constant
DEAR SIR/MADAM MY NAME IS ARKAPROVA BHATTACHARYYA.I AM A FRESHER INSTRUMENTATION ENGINEER.CAN YOU PLEASE SEND SOME QUESTION PAPERS OF GRADUATE ENGINEER TRAINEE EXAM OF DVC(DAMODAR VALLY CORPORATION).MY EMAIL IDs ARE arka_aec@rediffmail.com.
why we use 4-20 mA for calibration of the instruments.why we cant use 0-20 mA?
what is Instrument Schedule, and what it is mainly used for?
hey any one got the papers of SAIL and HPCL plz do help me by posting them to my mail ID's naren07_87@yaho.co.in, surenarendra@gmail.com
what is installation and commissioning of (fat & sat) of power plant dcs ? this question keeps in desirable conditions of one company .
what is temperature compensation?
what is the difference betwwen the 2wire level transmitter and 4wire level transmitter??and their applications also??
what is pico fuse? how this different rom othe fuses and how to locate it inside the card?
What is governor of turbine?
Lux meter is the measuring device to measure the lux level of lighting fixture. in industrial sector two types of lighting fixture is being used as street lighting purpose 1. HPSV (Sodium) and 2. HPMV (Mercury). HPMV having white light which is an combination of red, blue and yellow colour, while HPSV haivng Yellow lighting. in HPSV red & blue colour will be absent. during measurement of the lux level of HPSV and HPMV fixture. 1. Lux meter can measure the actual lux level of both fixture? 2. or it will show false reading for HPSV fixture light as it has only yellow light present. please give me answer
if a dp transmitter has range 100 in H2O and flow is 20mmcf and if the flow is changed to 25 mmcf then what is the formula to determine new range of transmitter
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)