Answer / baljinder singh
There is starter used for A.C. motor, according to
rating,the rating and starter used for A.C. motor give as
follow-
1 hp to 5 hp ----- only D.O.L. starter
6 hp to 20 hp ----- star-delta starter
more than 20 hp ---- auto transformer starter
| Is This Answer Correct ? | 93 Yes | 14 No |
Starter selection can be taken in accordance with the Motor HP rating.ie,
1. For 1HP - 5HP Motor :- DOL Starter can be used.
2. For 5HP - 20HP Motor :- Star Delta Starter can be used.
3. For 20 HP & above :- Auto Transformer Stater can be used.
| Is This Answer Correct ? | 24 Yes | 3 No |
For a 25 HP Induction motor one should use the star delta
starter. During the starting the motor draws 5 to 7 times
its normal current rating due to high inertia of its
armature. In the star circuit the Il=Tph as a result the
current is high. Its like moving a startionary object from
its position we require high force.
Pls add more.
| Is This Answer Correct ? | 19 Yes | 2 No |
UPTO 5HP DOL STARTERS USED ABOVE 5 HP STAR DELTA SARTER IS
USED BECUASE IT LIMIT THE STARTING CURENT
| Is This Answer Correct ? | 14 Yes | 5 No |
Answer / umesh joshi
Star Delta starter should ba used, because motor draws high
current in starting so we used motor should be in star and
after sometimes it is in delta so that that motor is ni
safe position
| Is This Answer Correct ? | 6 Yes | 2 No |
Answer / satya dev
Above than 10 Hp motor Only star delta starter can be used.
| Is This Answer Correct ? | 6 Yes | 13 No |
i have one source transformer with the capacity of 50KVA, connected with two loads 10kw and second one is 15kw.. how can i calculate first load in KVA and second one in KVA .. because Kva rating, power factor rating of of transformer is different from the load… there must be some way to calculate load KVA rating and power factor….
How to calculate per unit impedance of transformer?
electromechanical relay type identification example : type=tjmh t-stants for j- m- h-
How Size of Busbar is determined for a particular load.
what is active power and rective power and power factor
air condition capacity for masjad having 50feet in circal and 35 feet high
How can we calculate the Rating of DG Set for a 4 kw motor?
what is DG synchronization panel plz explain the working!!!!!!!
12 Answers Kirloskar, Lanco, MPS Techologies, Sedemac,
If more than rated DC voltage appears across trip coil of the breaker, what will happen? e.g. in 110V DC circuit system, if voltage across battery terminal showing 121 V
ITI r/tv trade APPLY (J.T.O VACANCEY) ALSO INCLUD AITT ELECTRONIC,WRITEEN XAM DONE 23.03.10 BUT NO RESPONCE WHY ANATHER ID gopal_gh007@rediffmail.com
what will be efficient rating of ac motor to lift a 10 kg wt of stone to 10 meter height with input 220V AC 50 Hz frequency???
how does the terminal voltage of transmission lines increase when a capacitor is connected???? This happens not only in transmission lines but also in all circuits. How??? When a capacitor is connected in a transmission line, capacitor also takes energy from the same supply. But how is it able to increase the terminal voltage??? Practically What sequence of events happen during increase in voltage???
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)