Answer / jayesh patel
Body earthing is used for body leakage current to earth &
not humen body harmful. Neutral earthing is used for
unbalance current pass through neutral & its goes to earth
& not effect on other phases voltages/load.
| Is This Answer Correct ? | 82 Yes | 4 No |
Answer / guest
The two types of earthing are Familiar as Equipment
earthing and Sysytem earthing.
In Equipment earthing: body ( non conducting part)of the
eqipment shold be earthed to safegaurd the human beings.
system Earthing : In this neutral of the supply source (
Transformer or Generator) should be grounded. With this,in
case of unbalanced loading neutral will not be shifted.so
that unbalanced voltages will not arise. We can protect the
equipment also. With size of the equipment( transformer or
alternator)and selection of relying system earthing will be
further classified into directly earthed,Impedance
earthing, resistive (NGRs) earthing
Both are equally importantand compulsory. As per your
requirement Earth pit value will be below 10 Ohms.
| Is This Answer Correct ? | 53 Yes | 3 No |
Answer / sarav
Ans 3 is mostly correct. But the value of the earthing is
below 2 Ohms.
| Is This Answer Correct ? | 19 Yes | 2 No |
Answer / riyadh
Star connection T/f's mid point of b/w two phase should be
neutral point . tat point is to be earthed ,
Body earth goes to ground the leakges in the T/f's to
protect human beings frm harmful
| Is This Answer Correct ? | 27 Yes | 15 No |
Answer / kunwar singh
Body Earthing : To ground any leakage current flowing in the e body of transformer & to protect human Body.
Neutral Earthing: To ground the unbalanced current in neutral.
The earth resistance should be below than 2 ohms.
| Is This Answer Correct ? | 7 Yes | 3 No |
Answer / nitin naik
1)Body Earting:- It is a part of earthing process were we
are connecting the metallic part of the equipment to the
general mass of the earth (earth is a zero potential) to
ensure any leakage current due to failure of the insulation
of the active conductor. If it is not ensured & suppose
there is leakage current it may cause electrical shock to
the person touching the metallic part of the equipment.
2) Neutral Earting:- It is being ensured & essential where
we are installing distribution transformer (Delta to star)
& Three phase neutral DG set, Neutral earting is the
process of earthing the star point of the secondary winding
of transformer & star point of the alternator winding to
the general mass of the earth. It is essential to eliminate
the return current in neutral due to unbalanced voltage &
further to eliminate unbalance potential between the
circuits.
Note:- In both the case earth setups resistance should
below 2 Ohms.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / pramod sharna
Basically earthing neutral earthing its protects fluctuation
of current and overloading and safety of equipment.
Body earthing is used to leakage of current.
| Is This Answer Correct ? | 3 Yes | 7 No |
i have three phase 25kva transformer but there is two phase line how can i connect to the two phase line?
What are the safety equipments you should use while you are in a hvac switch yard
1 Answers GPSC Gujarat Public Service Commission,
resistivity of copper
Good day everyone,currently in our premise we using 30kw slip ring motor with resistance bank which we use as forward and reverse at conveyor bar handling. So,my question is how do we calculate the resistance bank which is suit the motor. Kindly,assist me... thank you
which types of tests are required after commissioning of 6.6 kva tranformer?
What is the transformenr turns ratio.
why the electric train touches only one conductor n where is the neutral n it will be running 3-phase or 1-phase?
why transmission is done in delta system
What is the role of a Production Engg in a Industry?????
what type of insulation is used for over head lines?
what are the pecularity of shaver sockets ?
i am confused about generator. i have generator of 380 KVA that is 304 KW by that formula KW=KVA*0.8... then by this formula I=KW/V*1.732*0.8 the amperes are 528.673. so that is the load which i put on one phase of generator or this is total 3 phase load on Generator.......
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)