Answer / jayesh patel
Body earthing is used for body leakage current to earth &
not humen body harmful. Neutral earthing is used for
unbalance current pass through neutral & its goes to earth
& not effect on other phases voltages/load.
Is This Answer Correct ? | 82 Yes | 4 No |
Answer / guest
The two types of earthing are Familiar as Equipment
earthing and Sysytem earthing.
In Equipment earthing: body ( non conducting part)of the
eqipment shold be earthed to safegaurd the human beings.
system Earthing : In this neutral of the supply source (
Transformer or Generator) should be grounded. With this,in
case of unbalanced loading neutral will not be shifted.so
that unbalanced voltages will not arise. We can protect the
equipment also. With size of the equipment( transformer or
alternator)and selection of relying system earthing will be
further classified into directly earthed,Impedance
earthing, resistive (NGRs) earthing
Both are equally importantand compulsory. As per your
requirement Earth pit value will be below 10 Ohms.
Is This Answer Correct ? | 52 Yes | 3 No |
Answer / sarav
Ans 3 is mostly correct. But the value of the earthing is
below 2 Ohms.
Is This Answer Correct ? | 19 Yes | 2 No |
Answer / riyadh
Star connection T/f's mid point of b/w two phase should be
neutral point . tat point is to be earthed ,
Body earth goes to ground the leakges in the T/f's to
protect human beings frm harmful
Is This Answer Correct ? | 26 Yes | 15 No |
Answer / kunwar singh
Body Earthing : To ground any leakage current flowing in the e body of transformer & to protect human Body.
Neutral Earthing: To ground the unbalanced current in neutral.
The earth resistance should be below than 2 ohms.
Is This Answer Correct ? | 7 Yes | 3 No |
Answer / nitin naik
1)Body Earting:- It is a part of earthing process were we
are connecting the metallic part of the equipment to the
general mass of the earth (earth is a zero potential) to
ensure any leakage current due to failure of the insulation
of the active conductor. If it is not ensured & suppose
there is leakage current it may cause electrical shock to
the person touching the metallic part of the equipment.
2) Neutral Earting:- It is being ensured & essential where
we are installing distribution transformer (Delta to star)
& Three phase neutral DG set, Neutral earting is the
process of earthing the star point of the secondary winding
of transformer & star point of the alternator winding to
the general mass of the earth. It is essential to eliminate
the return current in neutral due to unbalanced voltage &
further to eliminate unbalance potential between the
circuits.
Note:- In both the case earth setups resistance should
below 2 Ohms.
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / pramod sharna
Basically earthing neutral earthing its protects fluctuation
of current and overloading and safety of equipment.
Body earthing is used to leakage of current.
Is This Answer Correct ? | 3 Yes | 7 No |
If a generator of generating station produces 100MW rated output then what will be the rating of the step-up transformer connected to it?
why skin effect is decreases with decrease with frequency? why skin effect occur
why the genearation of electricity always in form of sine wave only ??? why not cosine wave ???
We are designer please help me calculate the size of 11kv cables from step up transformer to M.V panel, total load is 5 mega watt distance 900 feet (used aluminum type cables) please provided formula for calculate the cable with example.
Why choke coil is connected in series with starter in tubelight??why starter is connected in parallel to tubelight??
why colour of electrical equipment( like transformer) is grey
which safety we have to take when we go for work?
what is the best electrical system i.e substation sytem of 11kv/.433kv for a township. if township have 300nos substation of 11kv. we have to go G.O.D.O. fuse unit or Compact Substation Unit. please reply Asap.
How we connect capacitors in Fixed Series compensation of AC transmission lines. Whether in parallel or in series?
ALONG WITH MEGGER TEST FOR CHECKING OF MOTOR ,WHY WE MEASURE FOR RESISTANCE AND INDUCTANCE?
wap to print prime number from 1 to 100 using c++
which one is more efficient, torq, power & ecnomy with the same frame size AC motor / DC motor?