We are using 3core 11KV HT cable for same phase for
generator outgoing, the cable leakage current is high and
cable heated overly what is the remidy, if we use the 3core
cable for 3phases the problem is solved are not?
Answer / k.prakashchandra
If earthing for pot heads is done at the both ends remove
one of them and watch.
Is This Answer Correct ? | 0 Yes | 0 No |