what is the formula for calculating milliampere at different
pressure points for eg 4-20 ma = 3-15 psi but if i have to
check the ma at 4.6 ma?
Answer Posted / abdulbasit137@hotmail.com
this is the one of the best formula for this situation
measuring value (1) - low ranmeasge value (1)/span
=
measuring value (2) - low range value (2)/span
u know span high value - low value 4 to 20 span is =16
3 to 15 span is = 12
simple
mv1 - lrv1 = mv2 - lrv2
span span
4.6-4/16= ?-3/12 = 4.3psi ans
| Is This Answer Correct ? | 1 Yes | 13 No |
Post New Answer View All Answers
Coal mill Instruments Equipments for cement plant And process diagram ?
IN CONTROL VALVE SPECIFICATIONS GENERALLY TERM " DE- 200" ."DM -400"USED,, WHAT IS DE/ DM STANDS FOR?
Q- What are the application in which PNP transistor is preferred over NPN ?
How will you calibrate PID controller? explain with example.
WHAT IS MEANT BY PROJECT MANAGEMENT STRATEGIES IN INSTRUMENTATION?
How to Calibrate Flow Switch in field
What is the advantage of using locally fabricated hook ups over Pre fabricated hook ups in process instrumentation?
We are using Rosemount 5400 series Radar Level Transmitters in all types of Sump Applications having oily water hdrocarbon petrochemical nature. What we are facing the problem frequently is that always getting reading frezzed at some value. If we do power recycling , sometimes it is working . then making same freezing problem. If anybody faced before such type of problem and also having solution , Please give the answer.
What are the type of bonnets in the control valves?
i have used level transmitter in starch cooking preparation tank. tank total height 2mtr.sometime LT display shows some error value when tank is fully empty and diaphragm side i already checked okay no problem in diaphragm area. field cable checked 24volt and mA shows correct value while tank empty mA is 4mA. 4mA i needed that 0% but display showing 10% or 15% percentage values are varying continously please give any good solution for me.....
What are primary elements of measuring pressure? Which type of pressure can be measured by these elements?
What is shielding effect?
detail of mass flow meter pricipal
what is the difference between -24 : +24 & 0:24 and where it use?
Why are the uses 24vdc in industries