what is the formula for calculating milliampere at different
pressure points for eg 4-20 ma = 3-15 psi but if i have to
check the ma at 4.6 ma?
Answer Posted / gunasekaran
4~20mA=3~15psi
4.6mA=?psi
psi =(mA -mA Zero)/(mA Span)×Range Span+Range Zero
4.6-4
psi = ------ x 12+3
16
0.6
psi = ---- x 12+3
16
psi = 0.0375 x 12+3
psi = 3.45
4.6mA = 3.45psi
| Is This Answer Correct ? | 19 Yes | 4 No |
Post New Answer View All Answers
what is dc moter.
Which topics are covered in Process Control?
Can combine control system for Emergency control system (ESD)and Fire & Gas System ( F & G) is possble to built and offer to client? Can such system is as per Norms in India?
Can I calibrate the Electromagnetic Flow Meter on line and How.
What is the difference between modbus,fieldbus & profibus
What is profibus?
What are different type of instrument cable
please someone tell me what is function of vibration sencer and how many types and how to control viberation.please. my id is jimmykhan077@gmail.com
Explain about the leakage class of the control valves
How to check vortex flow meter is in good condition while we do not having calibration setup?
why we us isolation barrier in hazardous area how it works to protect the area and please clarify its current flow.
How to calibrate an pressure gauge with yantrika test bench?
How to calibrate level transmitter with use of HART?
can u briefly explain aboutan aryton shunt multirange DC ammeter?
how to calibrate load cell