The open-delta connection it is actually 2 single phase transformer in series.
The voltage between two high voltage terminals it is 6600 V and each secondary
phase presents 110/√3 V.
If all three H.V.phases are connected the voltage between secondary terminals[in series] is 110/√3<0o -110/√3<120o=110 V<30o .
If the removed phase it is an extreme one then only one transformer stays connected [two voltages at ends] and the voltage is 110/√3 V.
If the removed phase it is the middle then both transformers stays connected with only one 6600 V and the voltage is 2*110/√3/2<0o=110/√3 V.
| Is This Answer Correct ? | 0 Yes | 0 No |
The open-delta connection it is actually 2 single phase transformer in series.
The voltage between two high voltage terminals it is 6600 V and each secondary
phase presents 110/√3 V[ some time even 100 or 110V].
If all three H.V.phases are connected the voltage between secondary terminals[in direct series] is 110/√3<0o +110/√3<120o=-110/√3 V<240o or oppositely connected 110/√3<0o -110/√3<120o=110 V<30o .
If the removed phase it is an extreme one then only one transformer stays connected [two voltages at ends] and the voltage is 110/√3 V.
If the removed phase it is the middle then both transformers stays connected with only one 6600 V and the voltage is 2*110/√3/2<0o=110/√3 V[or 110 V] for direct connection or 0 if they are oppositely connected.
| Is This Answer Correct ? | 0 Yes | 0 No |
i want to know is it possible to generate usefull power by coupling generator with motor & supply gives to motor by battery source then generator generates power. remove the battery source given to the motor & feed the supply from some of the generated power supply to the motor & motor runs continously. generator generate power contnously.is it possible ?
How to calulate cable size for 200KVA,160KVA& 40KVA load?
electical engg basic question
Difference between single phase rotary inverter and 3 phase rotary inverter
how much UPS neutral erath leakage current.
What is the problem if we connect a weak capacitor to the system? is that profitable or Loss?
difference between ac series and parallel circuit
how the arcing is made in ac electric arc furnace? ( between the three electrodes in any sequences or between the electrode & the charge(steel))
How Can Be Size Of Transformer Corelate With Freqvence?
Why transformer neutral earthing? What is advantages?
if we have a power factor 0.99 and we add a capacitive bank with it then what happen?
What are the neccessary safety arrangements before commissioning of HV substation?
Civil Engineering (5086)
Mechanical Engineering (4454)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)