In 6600/√3/110/√3v voltage transformer,how much output
voltage in open delta transformer,after removing 1-phase of
primary side on transformer?
Answers were Sorted based on User's Feedback
The open-delta connection it is actually 2 single phase transformer in series.
The voltage between two high voltage terminals it is 6600 V and each secondary
phase presents 110/√3 V.
If all three H.V.phases are connected the voltage between secondary terminals[in series] is 110/√3<0o -110/√3<120o=110 V<30o .
If the removed phase it is an extreme one then only one transformer stays connected [two voltages at ends] and the voltage is 110/√3 V.
If the removed phase it is the middle then both transformers stays connected with only one 6600 V and the voltage is 2*110/√3/2<0o=110/√3 V.
Is This Answer Correct ? | 0 Yes | 0 No |
The open-delta connection it is actually 2 single phase transformer in series.
The voltage between two high voltage terminals it is 6600 V and each secondary
phase presents 110/√3 V[ some time even 100 or 110V].
If all three H.V.phases are connected the voltage between secondary terminals[in direct series] is 110/√3<0o +110/√3<120o=-110/√3 V<240o or oppositely connected 110/√3<0o -110/√3<120o=110 V<30o .
If the removed phase it is an extreme one then only one transformer stays connected [two voltages at ends] and the voltage is 110/√3 V.
If the removed phase it is the middle then both transformers stays connected with only one 6600 V and the voltage is 2*110/√3/2<0o=110/√3 V[or 110 V] for direct connection or 0 if they are oppositely connected.
Is This Answer Correct ? | 0 Yes | 0 No |
What is corona? and what is the purpose of corona belt in substation ? why they connect these end of the buses ?
Im designing APFCR Panel for 600 KVAR.I need to calculate the full current so that i can choose the capacity of isolator/Breaker.Kindly suggest with formula.
How many types of faults are there in 3 phase power system?
100 MVA 3-phase alternator with earthed neutral has a reactance of 5 ohms per phase. what will be the fault MVA of generator.
What OPGW is better than Microwave or PLCC???
why ht motors are star connected?
what is 3 phase motors
what is the capacitance of a single conductor
Pls explan the OLR setting in VCB at HT yard
two way ckt diagram can be drawn by how many ways? give diagram
What does VVVF stands for in VVVF drive ? How does it differ from VVF drive?
VCB in closed position during opertion if vaccume break then what will happend? it has any protection ?