what is the formula to calculate kva genset required for a
given load in kw.
Answer Posted / virendra
Kva Required is = KW/0.8( Power factor )
& as the DG set is prefered to run at 80% load of the total
capacity then the Rated capacity is KVA/0.8
If the load is 100 KW rhen KVa is 100/0.8 = 125 KVa & the
rated kva is 125/0.8 = 156.25 KVA say 160 kva D.G set is
required.
| Is This Answer Correct ? | 34 Yes | 6 No |
Post New Answer View All Answers
Why 15Amp. MCB is suitable to carry load of 1.5Ton Ac please Explain?
What are differences between Voltage, EMF & Potential difference ?
how the testing of protection CT Testing done through Primary injection kit please describe in detail procedure...
placing earthing pit in pathway is correct or wrong??. placing earthing wireGI1/18 inside walls is correct or wrong?. explain!!!
What is miller crystal oscillator? Explain its operation?
what is the eight bit unit?
What do you mean by cogeneration? What its working principle?
If rotor works in clock wise what happens
how we can come to know that motor winding resistance which showing by DMM is right or wrong???is there any chart or something that we will compare & check???
Why did lightening arrestor solid copper rod head is sharp on mobile tower top?
which type of amplifiers are used in multimete?
explain different types of d.c motors?
what is the maintaining Cf in UPS.
draw the restricted earth fault protection circuit install on power transformer and identify its parameters and draw C/C curve of it
what is the effect of vector group while phase sequence of a generator changes,whether the vector group changes or not