what is the formula to calculate kva genset required for a
given load in kw.

Answer Posted / virendra

Kva Required is = KW/0.8( Power factor )
& as the DG set is prefered to run at 80% load of the total
capacity then the Rated capacity is KVA/0.8

If the load is 100 KW rhen KVa is 100/0.8 = 125 KVa & the
rated kva is 125/0.8 = 156.25 KVA say 160 kva D.G set is
required.

Is This Answer Correct ?    34 Yes 6 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

What was your role in the silicon evaluation/product ramp? What tools did you use?

2033


when will be the iocl interview results i faced interview on 8th september 2008 iam from electrical branch i faced interview for the post of electrical engineer??????????????????????//

2128


Can you used moeller lzm1 mccb in a dc system with 125vdc and 20ka short circuit current , beside is it have 24 or 48 volt shunt ? Beside how long current can through from An MCB shunt contacts? (like Z7-AS 24 V)?

2157


please send me latest & previous years question papers for IOCL Technical level questions

1958


Please send 110 kv sb station full single line drawing(sld)

2550


what is earth fault relay 64T, why it is used in main Incomer and neutral CT of Transformer.

3874


As i want some model question paper in basic computer science and history please send me immediately sir

1978


Dear All we are having a problem in G120 BOP showing alarm A0503, F0052, F0060 we can not remove fault alarm ,Please any body help us. kowsar

1972


XYZ

2227


sir i want previous entrance exam papers for written test

2249


What are the ratings of VCB, MCB, MCCB, SF6, ACB, and OCB?

1651


Draw the line diagram of diffretial relay connected to transformer?

2528


previous year paper of ntpc bhel for degree in electrical enng

3288


what is mean by restructuring power system?

2155


please send me last 5 year interview questions

2284