how to find the 2500 KVA transformer rated primary and
secondary volt and current?
Answers were Sorted based on User's Feedback
It is not possible unless u provide the input voltage u r going to give for the transformer and how much voltage u want as out put
however if u know input & output voltages primary and secondary current values can be calculated as fallows
2500 KVA 33KV/433V
Then primary current=2500/sqrt3*33=43.745A
And Secondary current=2500/sqrt3*0.433=3333.34A
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / abhi
It is not possible unless u provide the input voltage or
current than we calculat
formula
power(2500kva)=Voltage*current
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / santhosh
The Question itself is wrong. Only 2500KVA is not enough to
find out the voltage and current values.
| Is This Answer Correct ? | 2 Yes | 2 No |
why should series motor be started with load and shunt motor should be started without load??????
Which standard we are following earthing resistance test
how maney type tempereture measurement ?
What is the difference between earth fault and restricted earth fault protection?
How many kw will suply from one db
When Alarm report at LED,Alarm volatge is 11-13 Volt But LED is of 3 volt.then why not it burn?
what is the difference between transformer and amplifier ??
what is the difference between megger and earth resister ??
Lux meter is the measuring device to measure the lux level of lighting fixture. in industrial sector two types of lighting fixture is being used as street lighting purpose 1. HPSV (Sodium) and 2. HPMV (Mercury). HPMV having white light which is an combination of red, blue and yellow colour, while HPSV haivng Yellow lighting. in HPSV red & blue colour will be absent. during measurement of the lux level of HPSV and HPMV fixture. 1. Lux meter can measure the actual lux level of both fixture? 2. or it will show false reading for HPSV fixture light as it has only yellow light present. please give me answer
explain PV modules in solar energy generation.
The error in a single phase energy meter where pressure coil lags behind applied voltage by 88 degrees and pf is 1) upf 2).5lag
Is there any scope for an electrical engineer in MRF company......
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)