how to find the 2500 KVA transformer rated primary and
secondary volt and current?
Answers were Sorted based on User's Feedback
It is not possible unless u provide the input voltage u r going to give for the transformer and how much voltage u want as out put
however if u know input & output voltages primary and secondary current values can be calculated as fallows
2500 KVA 33KV/433V
Then primary current=2500/sqrt3*33=43.745A
And Secondary current=2500/sqrt3*0.433=3333.34A
Is This Answer Correct ? | 10 Yes | 1 No |
Answer / abhi
It is not possible unless u provide the input voltage or
current than we calculat
formula
power(2500kva)=Voltage*current
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / santhosh
The Question itself is wrong. Only 2500KVA is not enough to
find out the voltage and current values.
Is This Answer Correct ? | 2 Yes | 2 No |
mention hazard experienced during installation
can any one suggest websites having study maetrials for the electrical students?
How the electric train gets the supply of electricity? What is the return path of the current?
How much pole motor can be desion for 415 volt ,50 hz.Power supply. in pratical condition . Prakash veer singh
how much insulation resistance 11kv & 33kv under ground cable between earth to phase & phase to phase.
If i connect aload to phase taken from one transformer and neutral from another what will happen.
How to calulate Voltage Drop for perticular lentgh of busbar (Cu/ Al)?
What do you mean by ACB and VCB?
What is class X ct? What rare its uses?
WITCH CARDS IN USE IN FIRE CONTROL PANEL.
In Induction machines which type of emf is induced ( statically or dynamically)?
what is difference between bus coupler and auto transfer switch
0 Answers Dubai Properties Group,