when a motor is connected in parallel with the existing
motor the pf will change or not?
Answers were Sorted based on User's Feedback
Answer / indrajeet
It depends upon which type of motor you are connecting
means if you are connecting synchronous motor in parallel
then P.F.will improve.Instead of this if you connect
induction motor then the system P.F.will be lagging.
| Is This Answer Correct ? | 11 Yes | 0 No |
Answer / sreeknp
Explanation for the first answer
in syatem one motor is connected .if a second one of same
pf of earlier motor is connected parallel to the it then pf
will not change try with some simple figures
| Is This Answer Correct ? | 3 Yes | 0 No |
power factor will change due to the eq. of power factor
P=VIcos(angle beetwin v&i)
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / naresh chandra jha
it depend which type of notor you are connecting . for
example induction motor will operate in lagging power
factor, synchronous phase modilfier with under excited will
operate in lagging and when it is overexcited it will
operate in leading p.f .
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sreeknp
1' if the motor is of same pf --no change in pf
2'if second motor has lower pf then pf will lowered
3' if second motor has higher pf --pf will improve now it is
clear that may lower, higher or no change
so correct answer is sometimes it may chamge
| Is This Answer Correct ? | 0 Yes | 0 No |
how to calculate sizing of NGTR (Transformer rating,Loading resistor value and Current rating of resistor) and what is the X/R ratio. Details : 11kV,Capacitance 1.73532 micro farads,40kA for 1sec.
i alternator which of genarator used for excitor the what is reason?
Is electro plating what type of load whether resistive, inductive or capacitive loads
What are the transformer losses?
why the voltage transmission is always in a multiple of 11? e.g. 110 V, 220 V, 33 kVA, 11 kVA
How much allowable difference current between on three phases Dear sir, We have a 1870 KW HT motor, 11 Kv supply,FLA-120A,2870 rpm,2-pole squirrel cage induction Motor.And stator is connected in star connection with Liquid resistance stater to limit the starting current.It has coupled with Centrifugal air compressor.My question is it is loading 73% of FLA taking R-phase 86.7 A, Y-phase-85.4A,B-phase- 78.3A.why the B phase current is that much of difference.Is it allowable, or any one tell me how much allowable current.If any method to calculate.
what is the formula for building wiring to get the main breaker.
why the conservater tank alwes made upper side of transformer???
Dsitrubution transformer minimum IR value
What are options used for earthing the switchgear.
how to find out cable size if load is 2800 watts, 230 volts AC supply and load distance is 1800 meters
what are the merits and demerits of synchronous motor over an induction motor...??
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)