Answer / tuhin
an autotransformer will be smaller than an equivalent
conventional transformer. The reason is an autotransformer
essentially has one winding on a core, with one tap
including the whole winding, and another tap including only
part of the winding. In a conventional transformer, power
is transferred from one winding to the other by induction.
In an auto, some is by conduction, and some is by induction.
Here's an example comparison:
Say we have a 10MVA 100kV/50kV 3 winding auto transformer.
There are two parts of the winding - the series winding
(the section of winding between the 100kV connection and
50kV connection), and the common winding (the section of
winding between the 50kV connection to the neutral). If
powered at 10MVA (full load), there will be:
10M / (100k * sqrt(3)) = 57.7 Amps flowing into the
primary, and
10M / (50k * sqrt(3)) = 115.5 amps flowing out of the
secondary
So, 57.7A flow into the primary, down through the series
winding and out the secondary. At the same time 57.7A flow
up from the neutral through the common winding and out the
secondary, resulting in a total secondary current of (57.7
+ 57.7) = 115.5 (sorry, rounding is making my math look
wrong!).
Thus, the series winding is handling a total of:
(100k - 50k)* 57.7A*sqrt(3) = 5MVA, and the common winding
is handling a total of:
(50k - 0) *57.7A*sqrt(3) = 5MVA
So the series and common windings only have to be made to
handle 1/2 the total load(for this example - it is 1/2
because the primary / secondary voltage is 2/1). In a
conventional transformer, each winding carries the full
load (10MVA), because it operates on induction (no
conduction).
If the votlage ratio between primary and secondary is too
high, there is no real net savings in size (and thus cost),
so a conventional transformer is often used. The cutoff
point is around 4.
| Is This Answer Correct ? | 8 Yes | 4 No |
Answer / sivachandran
Auto transformer is a single winding transformer. In auto
transformer single winding is works both primary and secondary
| Is This Answer Correct ? | 4 Yes | 6 No |
WHAT IS THE WINDING PROCEDURE OF ELECTRICAL MOTOR
why choke is provided in the centre of the tube light?
what is the form factor of DC voltage
Technical specification of a wind farm
What is the latest generation of circuit breakers called?
3 Answers Epitome, Focus Energy, Jakson, KDC, L&T,
How many types of probe used in cro?
Please sent me some previous year question papers of BSNL-JTO telecom and RRB in ELectrical Engineering to varshashahi@yahoo.com
HOW TO CALCULATE HV TEST VOLTAGE FOR ELECTRICAL EQPT.
Why the Voltage rises when Leading Power Factor is occurs?
why most of the induction motors are delta connected?
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
What is the range of the stator resistance of 3 phase induction motor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)