why we are using auto transformer in sub station mostly???
Answers were Sorted based on User's Feedback
Answer / tuhin
an autotransformer will be smaller than an equivalent
conventional transformer. The reason is an autotransformer
essentially has one winding on a core, with one tap
including the whole winding, and another tap including only
part of the winding. In a conventional transformer, power
is transferred from one winding to the other by induction.
In an auto, some is by conduction, and some is by induction.
Here's an example comparison:
Say we have a 10MVA 100kV/50kV 3 winding auto transformer.
There are two parts of the winding - the series winding
(the section of winding between the 100kV connection and
50kV connection), and the common winding (the section of
winding between the 50kV connection to the neutral). If
powered at 10MVA (full load), there will be:
10M / (100k * sqrt(3)) = 57.7 Amps flowing into the
primary, and
10M / (50k * sqrt(3)) = 115.5 amps flowing out of the
secondary
So, 57.7A flow into the primary, down through the series
winding and out the secondary. At the same time 57.7A flow
up from the neutral through the common winding and out the
secondary, resulting in a total secondary current of (57.7
+ 57.7) = 115.5 (sorry, rounding is making my math look
wrong!).
Thus, the series winding is handling a total of:
(100k - 50k)* 57.7A*sqrt(3) = 5MVA, and the common winding
is handling a total of:
(50k - 0) *57.7A*sqrt(3) = 5MVA
So the series and common windings only have to be made to
handle 1/2 the total load(for this example - it is 1/2
because the primary / secondary voltage is 2/1). In a
conventional transformer, each winding carries the full
load (10MVA), because it operates on induction (no
conduction).
If the votlage ratio between primary and secondary is too
high, there is no real net savings in size (and thus cost),
so a conventional transformer is often used. The cutoff
point is around 4.
| Is This Answer Correct ? | 8 Yes | 4 No |
Answer / sivachandran
Auto transformer is a single winding transformer. In auto
transformer single winding is works both primary and secondary
| Is This Answer Correct ? | 4 Yes | 6 No |
when 20hp 3 phase motor start no load condition in star or delta connection.find current and write formula.(tariq)
what is the working principle/operation/theory of 3-phase rectifier power transformer used in cold rolling mills.
what will happen if a cw rotating altenator being synchronized to ccw rotating altenator
I would like to know that the fault curretn at base load and at 10% generation will be same? Fault level of BUS remain same with different generation?
whether fibre optic cable in high voltage earth conductor is used for protection circuits
can we use ACB for HT supply
what is power factor
Why is it that bus reactors are not accompanied by a neutral grounding reactor whereas a line shunt reactor is? PGCIL does so.
WHAT IS DIFFERENCE BETWEEN MANUAL CONTROL AND MAGNETIC CONTROL AND STATE ITS ADVANTAGE /DISADVANTAGE
What is domestic transformer? Draw the connection of domestic transformer.
In electrical what is earth(ground)connection, wht is the importance of it, why it is recomended to maitain below 3VAC between Neutral and earthspecially in PLC used machines?
what is the difference between bus-coupler and bus-riser
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)