What is difference between Dy11 & Dyn11 vector group
transformer. Can both these transformers operate in
parrallel.
Answers were Sorted based on User's Feedback
Answer / ravi
Winding connection designations
High Voltage Always capital letters
Delta - D
Star - S
Interconnected star - Z
Neutral brought out - N
Low voltage Always small letters
Delta - d
Star - s
Interconnected star - z
Neutral brought out - n
Phase displacement
Phase rotation is always anti-clockwise. (international
adopted convention)
Use the hour indicator as the indicating phase displacement
angle. Because there are 12 hours on a clock, and a circle
consists out of 360°, each hour represents 30°.
Thus 1 = 30°, 2 = 60°, 3 = 90°, 6 = 180° and 12 = 0° or
360°.
The minute hand is set on 12 o'clock and replaces the line
to neutral voltage (sometimes imaginary) of the HV winding.
This position is always the reference point.
Because rotation is anti-clockwise, 1 = 30° lagging (LV
lags HV with 30°)and 11 = 330° lagging or 30° leading (LV
leads HV with 30°)
To summarise:
Dd0
Delta connected HV winding, delta connected LV winding, no
phase shift between HV and LV.
Dyn11
Delta connected HV winding, star connected LV winding with
neutral brought out, LV is leading HV with 30°
YNd5
Star connected HV winding with neutral brought out, delta
connected LV winding, LV lags HV with 150°
" So there is no specification of Dy11.. it will be Dyn11 "
Is This Answer Correct ? | 63 Yes | 18 No |
Answer / pb
Dyn11 means Primary---Delta, Secondary---Star with neutral
brought out and secondary leading the primary by 30 deg
In case of Dy11 --- neutral is not brought out, rest
remaining the same as above.
Is This Answer Correct ? | 28 Yes | 6 No |
Answer / sunny
thanks ravi
i had searched all over the net but didn't cleared myself.....
very easy & understanding
Is This Answer Correct ? | 13 Yes | 7 No |
Answer / jim kirk
Mr Ravi
An excellent explanation - but there are DY11 transformers - we have two of them onsite
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kandavel .p
Thanks Mr Ravi i understood clearly ,your way of explanation is good thanks lot
Is This Answer Correct ? | 2 Yes | 3 No |
Why star delta starter is preferred with induction motor?
In wat way the power compensation takes place when a statcom is connected in a transmission line
why ground clearance of EHV line is more than HV line??
I am inpecting a 10kVA UPS what tests should i do and should i observe?
HOW DEFINE THE IP FOR ELECTRICAL EQUIPMENT AND WHAT IS THE IP OF PANELS USING IN HAZARDOUS AREA ?
when the diameter of the core and cable is doubled, the value of capacitance ?
How to select batteries required for ups and the inverter if we Known load? And how AH is selected of battery?
why power factor is lagging and leading(i.e -1to +1)
How to calculate HT XLPE CABLE for 11 kv / 433 v , 1500 kva oil type transformer system? plz provide step by step calculation
15 Answers Engineers India, Indian Railways, Polycab, Shashwat, Sitara Energy, Sonali Bank,
can any tell me how to do wiring connection in L&T 3ph 4wire E301 CT operated energy meter, what is P1,P2,P3,P0. M1,M2,M3, L1,L2,L3.
2 Answers Bhartiya International,
ADVANTAGES OF DIGITAL COMMUNICATION OVER ANALOG.?
why we have and use 3 phase not 2 or 4 or other in power system?