if u have to run a 300kw moter then what is ur choice HT or
LT switchgear & explain why?
Answers were Sorted based on User's Feedback
Answer / muralidaran - itc
It depends on Application. In HT conductor sizes will be
less & also motor will be more compact since current flow
will be less, but insulation level be more.
HT will be my choice, if speed controll is not required.
LT will be my choice, if speed controll is required (VFD)
Since HT VFDs are quiet high in cost.
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / vinoth
For 300 KW motor we can use LT switchgear. Current consumption of a 300KW motor will mot be more than 1000A. So LT switch gear is possible to use
Is This Answer Correct ? | 7 Yes | 3 No |
Answer / sadam hussain gaad
Depends upon application.
if all other motors are operated on HT/LT then 300 KW motor
should be opertaed on HT/LT respectively.
If your generation is HT and you want operate on LT then
you have to install VCB, Transformer, ACB and size of cable
will be more as compared to HT but less insulation will be
required.
If you want to operate 300 KW on HT then no need of
transformer,ACB, only XLPE cable will be used.
Is This Answer Correct ? | 1 Yes | 0 No |
Whats the type of current and potential transformers?
What is the difference between earth and neutral
4 Answers ABB, Tamboli Engineers,
WHY DG are rated in KVA or MVA ???., but ALL power plants are rated in KW or MW.,,?
What is the source of dependent source ?
Hello,l am complete dip and i was working maintance in ht dep again i study b.e completed again one year exp in ht totally two year i am ealigble in c license
when we have to purchase the transformer by own i.e how much load will preferred HT connection?
The D.C. spark test is applicable to single conductor cable & assemblies of insulated single conductor cables without insulation shield,metallic sheath or metalic armor?
What is the name of the winding from which the supply is taken for load connections?
WHAT IS THE DIFFERENE IN ACTION OF MCB,MCCB,RCCB
Why is it not possible to operate a star-delta transformer in parallel with delta-delta transformer?
Why MCCB is Getting tripped sometimes when there is no load in the Midnight ?
What is power focter ?