Pls tell me what is the exact current conducting capacity
of copper and aluminium cables?how much capacity of cables
need to 90kw induction motor&how?
Answer / nithyanandam
0.8A per sq.mm for Al. and 1.75A per sq.mm for Copper..
1hp motor takes full load current of 1.5A
1 Kw motor takes full load current of 1.99999A.
Therefore,
90 kw motor takes full load current of 180A.
so, 225 sq.mm aluminium or 102.8 sq.mm copper is the
suitable for 90kw motor
| Is This Answer Correct ? | 1 Yes | 4 No |
why we used to transmitt the power at higher voltage why not at lower voltage
i need previous entrence exam papers of nhpc.
What should be the Sandwitch type Al. bus bar capacity for 2 M.W.Gen. set, having continuous full load current- 3463 Amps,ambient temp.- 50 Deg. C., Required temp. raise-20 deg.C., it will run 24 hrs, 365 days on full load, required highly reliable.
Rules and standards of electrical control wiring ?
how to calulate short circuit current for the following: 1.cable connecting 11KV of 22KV/11KV transformer to 11Kv of 11KV/415V transformer 2.what cable size should i use.
in which material resister are made?
how is the testing of an REF relay? what are the test REF circuit having?
wat's the procedure to take short circuit current for cable selection
which fault is severe and why?between lll fault and lllg fault which fault is severe and y?
What r the specification furnishid in motor name plate?
what are the pecularity of shaver sockets ?
why we don't use earthing as neutral?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)