why frequency should be constant?
Answers were Sorted based on User's Feedback
Answer / mayilsamy ranganathan
we well known that all the generating staions are
interconnected by Transmission line and it is known as
interconnected grid system.The grid system is made to share
the load among all the powerstaion generators.
In a typical grid system the frequency is maintained at
50HZ,it means the generating power and power requirement of
the load is same.Hence in powerstaions the frequency is
monitored continuesly to findout the load requirement,if
the frequency dips below 50HZ,means the generator shaft
power increase and we have to give more input to generator
to meetout the extra load put on the shaft.Hence the
frequency is the measures of load,it is not constant,it is
continueously changing depending on load, we are trying to
bring it constant by maintaining generated power= Load
requirement.
| Is This Answer Correct ? | 29 Yes | 4 No |
Answer / nithi
In the power system most of the loads are induction motor
(nearly about 60%).so,apply this question for induction
motor.
For rated voltage,
below rated freq.: speed variation,high intake
current,over heating,insulation failure,core
saturation,harmonics production.
above rated freq.:drastic reduction in torque
production,speed variation.
so,frequency should be maintained constant.
| Is This Answer Correct ? | 8 Yes | 5 No |
what is the difference between DOL starter&star-delta starter& automatic star-delta starter
usually why bettery voltage are 1.5V, even if you open a 9V battery there are six 1.5V batteries in series. is it not possible to increase this voltage other than putting in series
What are Directly Exited Generators?
when an induction motor runs on load.at that time if we reduce the supply voltage the current increases.But when it runs without load,if we reduce the supply voltage the current also reduced.why?.i checked it practically also.
In a 3 phase 4-wire system. For a 3.5 core cable if all loads are single phase and balanced, what will be neutral current? will it be sum of all phase currents? Or it will be zero? And if loads are unbalanced what will be neutral current?
Define current?
What is effect of harmonic current (Draw by VFD) on power system/ electrical Equipments ?
how to calculate micom relay earth falt time and current sertting
why substation ratings are multiple of 11 means 11\33 kv substation
wht is an AVO metre. and whre it is used?
10Hp, 3-phase, 415v, 50Hz induction motor. The above motor is to run on Star-Delta connection, so how do i make following hardware selection 1) MCB, 2) Contactor, 3) Wire Gage (Depending on P-P current or Line Current), 4) OLR, Please tell in detail how to do the above, so as to get the ans. of it even if the Hp rating changes.
what are the types of electromagnetic forces developed in practical transformer?
0 Answers APC, BPCL Bharat Petroleum, Electrical Tech,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)