Classical power system stability was mainly focussed on
rotor angle stability but modern power system stability has
more focus on voltage stability.Why?
Answers were Sorted based on User's Feedback
Answer / iamdon
Majority of blackout/grid failure now a days is due to
voltage instability phenomenon.
This is because Modern power system is very vast and
interconnected to form a grid network.Also generation is
not sufficient to meet the load demand which is incresing
rapidly, due to which load end voltage drops.To maintain
load end voltage and power factor within permissible limits
shunt capacitors are used extesively at almost all load bus
bars(Over compensation),which has detrimental effect on
voltage stability.
At the time of peak load(load increase),the voltage at the
load end decreased so reactive power supplied by shunt
capacitors also reduced.So when we have most need of
reactive power supply,the shunt capacitor prove less
capable.
That's why modern power system satbility problem shifts
towards voltage stability.
Author:arbelectbit@yahoo.com
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / arvind
in todays time also rotor angle as well as voltage
stability anlaysis are been in focused, if rotor angle is
not into consideration then why so much transient analysis
is into picture.
| Is This Answer Correct ? | 1 Yes | 0 No |
Yes...Arvind.
Your proposition is right.
I had just made a relative analysis with two stabilities
involved.It does not means that the rotor angle is of no
importance today.It just establish the fact that now we
MORE FOCUSSED towards volyage stability.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / dharmesh
actualy both are cosider in today's power system the difference is rotor angle is for protection of generator and voltage regulation is for load regulation.
| Is This Answer Correct ? | 1 Yes | 0 No |
Between Turbo alternator and Hydro alternator which one is more difficult to cool and why?
WHAT WILL HAPPEN IF INPUT SUPPLY OF RCBO IS CONNECTED TO OUTPUT SIDE
what is the working principle of soft-starter & how it diff. from VFD ?????????
Can we get the shock if Power system is unearth means delta type take an rated voltage as 6.6 KV?
when generator of a power plant is not connected to grid , by increasing the mechanical torque speed of rotor increases but when it's connected to load instead of increase in speed current increases , why?
whenever a squirrel or a crow gets tangled near the out put of the feild transformer there is a discharge of 440 volts of current through the neutral due to which my appliances blow up causing a huge bang.will the RCCB help in these conditions
How LT megger works ?
Why the capacitor bank is keeping on for electricity supply and keeping it off for generator supply
Reversal of corrent feature in MCCB- What is reversalof current -explain broadly.
describe the Tranformer testing procedure
why contactor not provided between output of VFD and motor?
How to convert resistance value at 20 degree to 90 degree?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)