Answer / earnest
Boiler 3- element control system: (1)Boiler feed water (2)
drum level (3) steam flow
Is This Answer Correct ? | 33 Yes | 1 No |
Answer / visakh ctjv
Boiler 3-element system consists of boiler feed water
system, drum level system and steam flow system. working of
this system is based on cascade control
ie, output of one system is use as setpoint of another
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / ecxlsync
in boiler drum level control it uses the three elements
principle wherein it consist of Feed water Flow, actual drum
level and steam flow.
in the feed water line there are two Flow Control Valves (37%and 100%). the 37% is being controlled by single element
(single controller). the SP of single controller is the
actual pressure compensated drum level. if the steam flow
is more than 30% of its designed max flow, drum level
control will shift automatically to three elements control
which is in cascaded mode (two controllers). the output of
primary controller which is compensated by the steam flow
as feed forward control is being fed to the secondary
controller as setpoint for the feed water flow. the output
of secondary controller is sent to 100% FCV to manipulate
the feed water flow.
therefore, 3 elements control is to attain that feed water
flow will be equal to the Steam flow.
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / k.suresh
1)Boiler feed water 2)Drum level 3) Steam flow
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / naik muhammad
Most boilers of medium to high pressure today use a “3-
element” boiler control strategy. The term “3-element
control” refers to the number of process variables (PVs)
that are measured to effect control of the boiler feedwater
control valve. These measured PVs are:
▪ liquid level in the boiler drum,
▪ flow of feedwater to the boiler drum, and
▪ flow of steam leaving the boiler drum.
Is This Answer Correct ? | 2 Yes | 0 No |
Why Pressure Transmitter is NOT installed before up-stream of an ORIFICE PLATE? in a flow measurement.
how to calibrate control valves & power cylinders & ultra sonic level transmitters
what should be distance from tapping point to inallation place of instruments?
3 Answers Tasnee Petrochemicals,
which transister (npn or pnp) is used in vibration monitoring for negative voltage?
what is the difference between RTU & MTU in SCADA system?
How to Calibrate Flammable gas detector in field
how to control pid
I installed the smartplant instrument v8, but can not be opened, that always said: "INTools 2007 hardlock no found". So Could you help me how to do for that?
what is reset windup in integral control?
is manifold required for an integral orifice meter?
In s7-200 we use HMI TD-200C , what that C stands for........ plz reply
We Have Two Field bus Pressure Transmitters of Different Sensor Range (I.E One is of Lower range and Another is of Higher Range).Is same Process Line. My Question is Can i provide Saturation Limit to my field Bus Transmitter as We can provide Saturation current limit to HART Instruments. As During Low Pressure Both Working OK ,But During High Pressure, transmitter with Lower sensor range Goes to Fault mode as Beyond its Sensor Limit it can Measure, So may I provide Saturation point Some where to Suppress This Fault during High Pressure.