why middle phase should used for earth fault and other
phases used for over current in overcurrent and earth fault
relay?
Answers were Sorted based on User's Feedback
Answer / prasun bhaumik
It is a convention there will not be any problem
technically if we change that arrangement
| Is This Answer Correct ? | 7 Yes | 4 No |
Answer / vishal ingle
Not necessary to use only the middle phase.
our Back up protection cosist of two overcurrent elements
and one earth fault element.
under normal condition vector (IR + IY + IB) = 0
in fact middle phase is not used for earth fault prot.
Earth fault relay is connected between the star point of
all three phases (after O/C Relay) and the earth. if any
unbalance occurs, the unbalance current will flow through
the e/f relay.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / gunasekaran
on that point resiudual current is zero normally current sum
is zero at thatt point whenever balance is distrubed current
will flow
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / j.dev singh
for balancing of two phases current in relay.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / amrander singh
Please tell the answer Clearly......waiting..
| Is This Answer Correct ? | 0 Yes | 4 No |
Answer / pragnesh patel
This kind of arrangement is use for saving one over current
relay.
| Is This Answer Correct ? | 0 Yes | 4 No |
Answer / vinuram
first and 3rd phases are having voltage and current
flactuation.
| Is This Answer Correct ? | 0 Yes | 7 No |
what is the difference between fault current ant short circuit current?
define briefly the function of an ac electric generator (alternator)?
What is value of earth resistance required for substation and equipment earthing and what are the reference guidelines
what is max. continous current of LT side of distribtion transformers? ie for25kVA, 63kVA, 100kVA, 200kVA etc
Residual voltage & residual current used in which protection?
5 Answers Qatar Gas, Reliance, Transformers and Electricals,
How to calulate cable size for 200KVA,160KVA& 40KVA load?
difference b/w bus bar and tie line?if possible explain with eg:
What is the out put of a CT? How the ratio is decided ?
i want design of D.C.MOTOR 1HP 960RPM AND 2HP 960RPM ITS URRGENT
ROC converges if pole and zero lies inside a) origin b) z=1 c) pole d) zero ? Explanation please? if ROC does not converges then?
What are the fire Estingushers use in electrical fire?
can we use ps class in combination with protection class in differential protection and over current protection.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)