A 11 KV motor is working. if the supplay is fail. what
will happened with it's breaker? Trip / remain the same
condition?
Answers were Sorted based on User's Feedback
Answer / nishad
The Motor will surely trip becaue by the sensing of under
voltage relay, it will give the trip command to the
breaker. once the breaker trip motor also trip. well in
cause of a small Voltage dip motor may not be trip. because
it's related to the setting of undervoltage relay.
somewhere it is set 2 second ( as per company's requirment)
if the power failure is more than set time of undervoltage
relay, motor trip
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / k.prakashchandra
It will trip,if the breaker of motor has a voltage operated
hold coil which also provides protection against low voltage.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / asish
the motor will not be tripped as there is no fault as only
supply is off.
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / rajesh
as the supply power is constant, infinitely high current will flow through the circuit and hence the circuit breaker will trip.
| Is This Answer Correct ? | 0 Yes | 2 No |
how to determine Sq.mm size of finolex power cables.
NOW A DAYS THE POWER SUPPLY IS VERY LOW.SO THE FLURESCENT TUBE LIGHTS ARE VERY DIM.IS THERE IS ANY WAY TO INCREASE ITS BRIGHTNESS?FOR EXAMPLE ANY CONVERTER,CONDENSER?
What is deference between MCB & MCCB & ISOLATOR
0 Answers Prakash Industries, Standard Chartered,
percetans
how was your last weekend.
why DOL starter is use in induction motor as it is not reduce the starting torque
What are pre paid energy meters ? How it works ?
At site, we have 30Kw motor (3 phase, 400V,50Hz) and FLC 54A as per the nameplate. At the time of starting it draws 840A instead of 390A (7.2%). As per the data sheet also its 390A starting current. it thru a dol starter from the MCC. can anyone tell what is the problem in the motor
What is the difference between PLC and Embeded system
what is significance of B-H curve? how it differs form ordinary transformers to Amorphous Transformer?
What is the difference between multimeter
E.B sending end to receiving end 33kv ug cable laid 8Km,receiving end to ss1,ss2,ss3,ss4 all are Approx 800 Mtr,can go for 33KV to 430V or 33kv to 11kv in receiving end and 11kv to 430 near ss ,which one is good for technically and economically.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)