A 11 KV motor is working. if the supplay is fail. what
will happened with it's breaker? Trip / remain the same
condition?
Answers were Sorted based on User's Feedback
Answer / nishad
The Motor will surely trip becaue by the sensing of under
voltage relay, it will give the trip command to the
breaker. once the breaker trip motor also trip. well in
cause of a small Voltage dip motor may not be trip. because
it's related to the setting of undervoltage relay.
somewhere it is set 2 second ( as per company's requirment)
if the power failure is more than set time of undervoltage
relay, motor trip
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / k.prakashchandra
It will trip,if the breaker of motor has a voltage operated
hold coil which also provides protection against low voltage.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / asish
the motor will not be tripped as there is no fault as only
supply is off.
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / rajesh
as the supply power is constant, infinitely high current will flow through the circuit and hence the circuit breaker will trip.
| Is This Answer Correct ? | 0 Yes | 2 No |
EXPLIAN THE IMPORTANCE OF POLY PHASE CIRCUIT.
what is the purpose of using filters in a protective relaying scheme?
where to use CT and PT?
We in my plant one of the transformer showing neutral to earth voltage is 22V how to solve it
What core magnetic balance test of transformer? How to do this test in a three phase Star delta (star-LV, Delta-HV) transformer? How to measure and where to measure? thanks and regards Austin
22 Answers Neutech, Power Grid, TSSPDCL,
in india single phase is 230v and three phase is 440v but in other countries single phase is 110v and three phase is 380v why..?
what is d check in dg 1500kva
How Humming noise generated in starter motor which was used the start the engine in a vehicle/car/Truck?.Moreover Starter motor was operated in DC power supply. Can you guys clarify ?
(1)The demand for electricity , the amount of renewable generation available, the amount of fossil fuel generation available and the cost of the fossil fuel generation are shown in table below period(hrs) demand(MW) renewable (MW) fossil- fuel(MW) cost of fossil fuel(MW) 00.00 - 01.00 2000 1800 2000 30 01.00 - 02.00 2300 2500 2000 30 02.00 - 03.00 2500 2700 2100 45 03.00 - 04.00 2900 3100 2100 50 04.00 - 05.00 2700 2600 2500 45 05.00 - 06.00 2400 2000 2700 50 06.00 - 07.00 2200 1800 2000 36 07.00 - 08.00 2100 1600 2000 36 Assuming that the renewable generation incurs zero cost, determine an optimal generation schedule(specifying the amount of renewable generation and fossil fuel generation used in each period, the cost for each period and the overall cost for 8 hours.)
Formulae for calculating the transmission line losses for different voltage levels
what is interpose vt where it is used and y it is used?
What was your role in the silicon evaluation/product ramp? What tools did you use?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)