Why 3 over-current and 1 earth fault relay is used on
primary side of transformer? Why 2 over-current and 1 earth
fault relay in used on secondary side of transformer?
Answer / ronik
1)The reason when a double line fault occurs on secondary
side then if the transformer is of DY11 type then if 2
over-current relays are used on primary side instead of 3
O/C relays then the phase in which no relay is placed will
carry double the fault current and the in current in the
either phase will be low enough that a relay can pick
up...and meanwhile the damage will be done to the system...
2)Moreover the ground fault on the secondary side will not
have any effect on the earth fault relay on the primary side...
3)on secondary side each and every fault will be detected by
the 2 O/C and 1 earth fault relay easily...
Is This Answer Correct ? | 4 Yes | 4 No |
what is meant by neutral Ct of a transformer and how it connected in transformer
how we control the magnitude of a generator output
What is the lower limit of megger value for 66/11KV power Transformer ?
7 Answers MSETCL Maharashtra State Electricity Transmission Co Ltd, Torrent Power,
what is purpose of using neutral grounding transformer in generators??
Does Rheostat can use for power factor correction?
how to calculate the current carrying capacity of a conductor. How it is related to diameter of cable or conductor
difference between the earthing,grounding and neutral
what is the meaning of improving the power factor (give technical ans not therotical)
why the electrical plug point pin(earth) size in max
1 Answers Autoneum Nittoku, Bajaj,
What kinds of decision are made about CT from it's Knee point(voltage & current)?
In hydro plant,generally we install vertical hydro generators..why dont we recommend horizontal one??
working of diesel generator ?