For a DY11 lighting Transformer on primary side whee to
connect fourth lead? from nuetral or from ground?
Answers were Sorted based on User's Feedback
Answer / thiyagarajan
For Dyn11 its primary will be delta and secondary will be
star to give path to the unbalance current to earth
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / irshadahmed syed
For DY connection Primary will be in Delta connection so their will be No Neutral option in Delta connection so fourth lead should be taken from ground.
| Is This Answer Correct ? | 0 Yes | 0 No |
which mm cable should be used for 1.hp immersible pump motor for the distance of 330 metres?
what is the difference between ups & inverter
4 Answers Cushman Wakefield, Dana Group,
if we give 60 hz single phase supply to the transformer used in europe , than what will happen
Dear Brother can u tell the proper size selection of cable & the fault level calculation of braker, busbar etc. pls mail me at azeemk30@gmail.com
what are the possible reaons & remedies if resistance of NGR getting heat up
which type of insulation are used on 132kv transmission line
when 40 watts and 60 watts bulb is connected in series, which bulb glows brightly ?
what are the main hormonics in ac?
What is VFD, and how its work
What is the similarity and what is the difference between relays and PLC?
which is the best book of electrical objective for placement
Would you recommend to replace all oil filled cables with xlpe cable for hv transmission with the current technolgy for xlpe cable?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)