For a DY11 lighting Transformer on primary side whee to
connect fourth lead? from nuetral or from ground?
Answers were Sorted based on User's Feedback
Answer / thiyagarajan
For Dyn11 its primary will be delta and secondary will be
star to give path to the unbalance current to earth
Is This Answer Correct ? | 7 Yes | 2 No |
Answer / irshadahmed syed
For DY connection Primary will be in Delta connection so their will be No Neutral option in Delta connection so fourth lead should be taken from ground.