In CDG type IDMTL realy O/L , E/F, O/C which are used for
out going feedrs,on R-phase o/c element, Y-phase , e/f
elecment and on b -phase o/c element will be connected .
Why the earth fault on center phase only, why not on other
two phases?
Answers were Sorted based on User's Feedback
Answer / sathiyaseelan.m
I thing you may misunderstand that.
As per your Qtn.: It has 2 O/c 1E/F
That means Over current b/n R&Y & Y&B so 2 O/c and this two
are eough to protect the Entier system from O/C.
And the earth fault sences from all phases unbalanced load
only. That means Internaly all are taken for refarence
| Is This Answer Correct ? | 12 Yes | 2 No |
Answer / gova
This is called 2 O/C+1E/F relay scheme.This scheme is used
mainly where the transformer connection is Dyn11.
please refer the current distribution in this transformer
when a fault occurs in feeder.
This scheme will be sufficient to clear the faulty
section.But nowdays 3O/C+1 E/F relay scheme also used in
many places
gova
| Is This Answer Correct ? | 6 Yes | 2 No |
how oltc works in rectiformers of higher rating (27 mva,200v dc,120kamps) please provide me full information with diaggram.
what r the sizes of CB's? how to select CB's?
For a 50MVA (138/69/13.8 KV) transformer, what would be the maximum demand in order not to exceed 80% of its operating capacity.
Draw SLD for a panel has 500A Bus Bar rating, with 4 outgoing, each is 80 A (load current), showing the transformer and capacitor bank rating.
what is principle of DG
what are the types in Relay?
How to differentiate 220 Kv & 132 Kv line transmission tower if there are no specifications given on towers?
how to synchronize 3 phase slip ring induction motors of different ratings.
Advantages/Disadvantages of earthing of neutral bus on MSB instead of separate neutral earthing for transformer/DG sets feeding to MSB
what is the difference between CT and CVT in EHV Sub Stations
4 Answers Hofincons, Lanco, TATA,
what is meant by fuzzy logic? what is fuzzification and defuzzification?
WHY DO VOLTAGE TRANSFORMERS FAIL DURING EARTH FAULT IN THE DELTA CONNECTED 6.6KV ELECTRICAL SYSTEM
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)