hi engineers,if suppose distribution is going to two diff
village mistakenly they r interchange the neutral of twowhat
happen?
Answers were Sorted based on User's Feedback
Answer / balaji
1.Normally for villages we will use 415 volt supply.if we
use two different transformers we cant interchange neutral
because in transformer secondary side neutral will be
earthed.if you interchange means circuit will not closed.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / b.k.rai
if single phase supply 230vac,then nothing happens
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / vipul bhavsar
In distribution if neutral interchanged but both is healthy
nothing happened,in case one neutral got loosed or opened
than unbalanced voltage will be induced in each phase and
it may be in KV for Milli sec. also so will fused electronic
component also, you also hear that due to GEB high voltage
television got fused this happen due to neutral shifting.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / rajesh tewari
plz explain the question....that whose interchane 1
phase..2phase...3phase and neutarl
| Is This Answer Correct ? | 1 Yes | 0 No |
what is real , reactive and apparani power
A genarator is connected through a 20MVA ,13.8/138 KV stepdown transformer to a transmission line. at the reciving end of the line a load is supplied through a step down transformer of 10MVA,138/69 KV rating .A 0.72 PU load evaluated on load side transformer ratings as base values ,is supplied from the above system for system base values of 10 MVA and 69 KV in load circuit the value of the load in generator circuit will be ...........
1 hp single phase motor is more likely to get hot thsn inone hp 3 phase motor its true or false? If true why?
3 Answers Focus, Focus Energy,
why we are using the ac supply in domestic purpose, why don't use dc supply.
How can we deside Short Ckt level of electrical System,Breakers etc.please provide formula to find SC of HV side & LV side
what will happen when square wave is fed into input side of 3kva transformer and what you will get on output side.
why holding contact is not using in VCB and ACB breakers?
what is volt drop formula?stm
why generator and t/f ratings given in kva?
please design a rectifier with batteries for below requirement and also explain how you calculate this solution, Load = 700Amp DC Backup time = 6 hour. please explain briefly ?????
what happen when power factor of 2 parallely operated transformer become equle?
in case dc we mark as + ve & -ve..but in case a.c. we mark as ph&N...Y LIKE PLZ TELL ME
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)